Is it possible to interlock between ACB & MCCB?
Answers were Sorted based on User's Feedback
Answer / jesudoss
can ..u can use electrical interlock acb between mccb.ACB
should have NO,NC contacts.now new MCCBs also have NO,NC
contacts(ex:ABB TMAX - this MCCB have
charging,closing,opening coils also).
| Is This Answer Correct ? | 15 Yes | 0 No |
Answer / g.pattabiraman
For positive, fail safe interlocking, between ACB and MCCB to prevent both getting ON at any given time,
use of UNDER VOLTAGE COIL, along with auxiliary switches of the breakers is needed
ACB under voltage coil in series with MCCB aux. N.C contact
and MCCB under volt coil in series with ACB aux. N.C contact will give this fail safe protection
Motor operation or manual operation are user choice
| Is This Answer Correct ? | 4 Yes | 0 No |
i want to know that what is the eligibility critaria for ongc exam?
In generation,transmission and distribution voltage frequency is either 50HZ or 60 HZ;why are only these frequencies?
why rating of alternator in kva & induction motor in kw
how the alternator transfere mechanical energy to electrical one ??
Which fault is caused by lightening and thuderstorm a. Line to line fault b. Single line to ground fault c. Double line to ground fault
What range of speed can you get with the armature control method of speed control of d.c. Shunt motor?
Why derivative controller is not used in control systems?
which motor have relatively high power factor and what is reason for have high pf? 1.capacitor run motor 2.shaded pole motor 3.capacitor start motor 4.split phase motor
how to calculate no load losses units comsumed by transformer
What cmos is and its benefits?
why ct is testing using dc.. y cant we use AC insted of dc on POLARITY TEST.
Dear Sir, we met a disaster with our 62.5 kva genset, after rewinding we informed by our contract engg that due to return current coming in neutral & impropper earthing this happend. But after all set up & load balance we checked & found again we have about 20 to 32 amp return current on neutral. we have 12 airconditioner + 12 mini fridge on single phase line. Pl suggest any idea to solved this problem
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)