why neutral busbar size is half of the phase busbar size in
control panels
Answer / abdul samad
If ur Load is balanced in three Phase supply system Neural
current is Zero . neutral current is always depend on the
Unbalance load. So in Case of 3 phase system neutral bus
taken half of Main bus.
but in case of 1 phase supply system neutral is the return
cunductor and phase current will be equal to neutral curent.
so In 1 phase neural would be of same size.
as In three phase, current in neutral in one third
of phases so conductor size is less. but in single phase neutral conductor size should be same as phase conductor size
Is This Answer Correct ? | 6 Yes | 4 No |
how choose conductor &caple&wire depending upon the load
wat is d first thing to be seen 2 lay a cable in a particular area??
what is RCBO?
what is the setting of locked rotor in HT motor ? (answer expecting in percentage)
2 electric bulbs of 100w,200V are put in series & the combination of each bulb is supplied to 100 V . the power consumption of each bulb will be????????
Which is the largest hydropower station in the world?
What is the difference between vector surge relay (78) and Pole slip relay (98G)
can any tell me how to do wiring connection in L&T 3ph 4wire E301 CT operated energy meter, what is P1,P2,P3,P0. M1,M2,M3, L1,L2,L3.
2 Answers Bhartiya International,
what is V.L.F. testing of power cable? do you know the voltage ratings, like for what rating and size of cable what rating of V.L.F. testing is used?
what is difference between 9kv 5ka surge arrester and 9kv 10ka surge arrester.
How to calibrate or test an LT Air Circuit breaker 440 volts, 35 KA, 800 Amps ?
What is the generating voltage of a power station consided generally?