Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


we have taken HV test of 2.5 k and Megger test on 11 kv HT
cable.here it shows no fault but when we are charging the
same cable with 11 kv supply why the VCB 11 kv gets tripped
can anybody define the possible cause of fault ?

Answers were Sorted based on User's Feedback



we have taken HV test of 2.5 k and Megger test on 11 kv HT cable.here it shows no fault but when ..

Answer / shariff

The 11kV cable will be designed for morethan 12kV and the
megger applied voltage is just 20% of that rating.. so the
cable insulation might be withstanding at that vg but it is
failing at higher voltage.. So go for the Hi pot test with
DC pulse nearly 15kV...

Is This Answer Correct ?    4 Yes 1 No

we have taken HV test of 2.5 k and Megger test on 11 kv HT cable.here it shows no fault but when ..

Answer / shariff

The 11kV cable will be designed for morethan 12kV and the
megger applied voltage is just 20% of that rating.. so the
cable insulation might be withstanding at that vg but it is
failing at higher voltage.. So go for the Hi pot test with
DC pulse nearly 15kV...

Is This Answer Correct ?    1 Yes 1 No

we have taken HV test of 2.5 k and Megger test on 11 kv HT cable.here it shows no fault but when ..

Answer / nagesh.patwari

Check out the control circuit. And every possible relevant thing in panel cable breaker.... Thoroughly.

Is This Answer Correct ?    0 Yes 0 No

we have taken HV test of 2.5 k and Megger test on 11 kv HT cable.here it shows no fault but when ..

Answer / shariff

The 11kV cable will be designed for morethan 12kV and the
megger applied voltage is just 20% of that rating.. so the
cable insulation might be withstanding at that vg but it is
failing at higher voltage.. So go for the Hi pot test with
DC pulse nearly 15kV...

Is This Answer Correct ?    0 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

in a large three phase induction motors usually the value of full load slip is

1 Answers   PSEB,


Saving in copper achieved by converting a 2 winding transformer in to an auto transformer is determined by A voltage transformation ratio B load on secondary C quality of core material D size of transformer core

0 Answers  


Why electrical power generation and transmission done in 3 phase system not more than 3 phase ?

0 Answers  


What is the Gap Should maintain for HT cables crossing of LT Cable?

2 Answers  


We have two 1 phase heating coils having same resistance of 25ohm, but during operation one takes 3A and other 6A Is it posiible Pls. explain

5 Answers   Bhel,


1.what is the difference between transformer differential and busbar differential.2)why we are using 2 slope for trafo diif and 1 slope for busbar diff.3)what is the purpose of metrosil and stabilizing resistor in high impedance relay circuit.4)how metrosil reduce the peak volage.5)what is the funtion of stabilizing resistor

0 Answers  


Advantage of LT panel vs HT panel ?

1 Answers   HCL,


What is meant by IP55 motor.Where it is used?

2 Answers   Zuari,


How many power required for 1.5 to Airconditioner?

1 Answers   College School Exams Tests,


what is the necessity of under ground cables ??

0 Answers  


If 22 KV HT line, Current transformer is 25/5 then how to calculate multiplying factor.

0 Answers  


how many kw = one ton air condition?

2 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)