we have taken HV test of 2.5 k and Megger test on 11 kv HT
cable.here it shows no fault but when we are charging the
same cable with 11 kv supply why the VCB 11 kv gets tripped
can anybody define the possible cause of fault ?
Answers were Sorted based on User's Feedback
Answer / shariff
The 11kV cable will be designed for morethan 12kV and the
megger applied voltage is just 20% of that rating.. so the
cable insulation might be withstanding at that vg but it is
failing at higher voltage.. So go for the Hi pot test with
DC pulse nearly 15kV...
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / shariff
The 11kV cable will be designed for morethan 12kV and the
megger applied voltage is just 20% of that rating.. so the
cable insulation might be withstanding at that vg but it is
failing at higher voltage.. So go for the Hi pot test with
DC pulse nearly 15kV...
| Is This Answer Correct ? | 1 Yes | 1 No |
Check out the control circuit. And every possible relevant thing in panel cable breaker.... Thoroughly.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / shariff
The 11kV cable will be designed for morethan 12kV and the
megger applied voltage is just 20% of that rating.. so the
cable insulation might be withstanding at that vg but it is
failing at higher voltage.. So go for the Hi pot test with
DC pulse nearly 15kV...
| Is This Answer Correct ? | 0 Yes | 1 No |
in a large three phase induction motors usually the value of full load slip is
Saving in copper achieved by converting a 2 winding transformer in to an auto transformer is determined by A voltage transformation ratio B load on secondary C quality of core material D size of transformer core
Why electrical power generation and transmission done in 3 phase system not more than 3 phase ?
What is the Gap Should maintain for HT cables crossing of LT Cable?
We have two 1 phase heating coils having same resistance of 25ohm, but during operation one takes 3A and other 6A Is it posiible Pls. explain
1.what is the difference between transformer differential and busbar differential.2)why we are using 2 slope for trafo diif and 1 slope for busbar diff.3)what is the purpose of metrosil and stabilizing resistor in high impedance relay circuit.4)how metrosil reduce the peak volage.5)what is the funtion of stabilizing resistor
Advantage of LT panel vs HT panel ?
What is meant by IP55 motor.Where it is used?
How many power required for 1.5 to Airconditioner?
1 Answers College School Exams Tests,
what is the necessity of under ground cables ??
If 22 KV HT line, Current transformer is 25/5 then how to calculate multiplying factor.
how many kw = one ton air condition?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)