why sec of ct should be kept shorted
Answers were Sorted based on User's Feedback
Answer / vishal ingle
the CT works on the principle of
Primary AT = Secondary AT
When current is flowing through primary, there must be
path for the secondary current to flow.
Else heavy ovevoltage will be induced in the secondary
winding which is sufficient for insulation failure and
busrcting of CT.
Hence CT secondary should always be short circuited
| Is This Answer Correct ? | 5 Yes | 3 No |
Answer / k
The output voltage will rise trying to develop current until
it reaches the saturation voltage of the coil at that
frequency. At that point, the voltage will cease to rise and
the transformer will add no additional impedance to the
driving current. Therefore,the output voltage of a current
transformer will be its saturation voltage at the operating
frequency.
| Is This Answer Correct ? | 0 Yes | 1 No |
How we calculate the average power factor if the one phase is lag and another one is in lead?
How will you calculate the correct KWH value if your CT is 600/5 and your KWH meter is rated for 100/5
Can anyone tell me some hints about what type of questions are asked by the interviewer by an Electronics engineer when company is installing an IPP and wants a team of engineers?
i am an maintenance engineer. one distribution board have 5 feeder. recently its ELR trips frequently, but it take some times after trip( 10min,20min..)but 3 feeder no load. two feeder only loaded. i checked one feeder IR value all values are above 50Mohm.but B phase to Earth is only 9Mohm.any problem about low value
When distance between two pulleys is not fixed, the tension of belt is adjusted by a) driver shaft b) driven shaft c) adjustment screw d) belt
in a solar power plant,we are going to step up the voltage 350V to 33kv, and to 132kv GSS. i want to ask that if it is possible that 315v/33kv is not possible because we also use 315v/11kv. or it should be 415v/33kv? is it effects generation or losses? the second question is-generation is depends on LV winding? or LV winding design for generation voltage?
what is mean by lookup table in microprosser.
How to Calculate Stc Rating of an indoor type VCB Panel? What is a full form of STC?
how can we minimize the off load losses of a distribution transformer which is required to be energized 24x7 ?? capacity of the T/F is 1250 KVA and off load losses are around 2.0 KW.. can we use capacitor bank at the secondary of such a T/F to overcome off load losses? please elaborate briefly...thanks
What is the difference between a Root Locus plot and a Bode plot?
neutral earth resistance testing is it possible for transformer while in load condition
how wud i know that whether i have to use unitized package substation or transformer?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)