Answer / vishal ingle

the CT works on the principle of
Primary AT = Secondary AT
When current is flowing through primary, there must be
path for the secondary current to flow.
Else heavy ovevoltage will be induced in the secondary
winding which is sufficient for insulation failure and
busrcting of CT.
Hence CT secondary should always be short circuited

Is This Answer Correct ?    5 Yes 3 No

why sec of ct should be kept shorted..

Answer / k

The output voltage will rise trying to develop current until
it reaches the saturation voltage of the coil at that
frequency. At that point, the voltage will cease to rise and
the transformer will add no additional impedance to the
driving current. Therefore,the output voltage of a current
transformer will be its saturation voltage at the operating
frequency.

Is This Answer Correct ?    0 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

how is the cable tray designed & how its total length is calculated for an Industrial plant Say for Ex. (500KW Motor Load)

0 Answers  


what are the different kind of cables used for transmissions?

0 Answers  


Does Rheostat can use for power factor correction?

1 Answers   GOMS,


if we have 320KVA Genset kindly advice how much load we can put it.

0 Answers  


Double Busbar Scheme for outdoor switch yard system (132kv) step up power plant Hi friends 1. in this system both busbars energized all the time. 2. what is the meaning of main BB and transfer BB, 3. step up transformer connect main bus bar all the time or both BB connected through DS switch . 4.bus sectionalization means ? thank you.

1 Answers   ABC, Gael,






we have earthmat at 110KV substation.we would like to take earth resistance.b some says that by connecting earth megger terminals (C1,P1) at middile point of earthmat (at riser) will cause voltage gradient at other earthmat nods and dont get exat earth resistance.when connecting at end nods will get exat value . is it correct .please explain

0 Answers   TNEB Tamil Nadu Electricity Board,


what is the job description of a LOW CURRENT ELECTRCIAL ENGINEER in a industry?

1 Answers   BTAT, Powercraft, Prince Glass, Sterling,


What is the difference between CT for protection and Ct for metering?

16 Answers   BirlaSoft,


What is the Impedance, inductive reactance calculations

0 Answers  


what is the unit of current

12 Answers   RRB,


16kv transformeris stolen in my village.and department is not taking action.then what should i do.any shortcut .please help any idea

1 Answers  


What is differential relay ? where it can be used?

1 Answers   Scope International,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)