What is AVR in Turbo generator in Thermal power plant?
Answers were Sorted based on User's Feedback
Answer / rohit chandan
The main purpose of Automatic Voltage Regulator (AVR) is to
control the excitation to limit the terminal voltage of
synchronous generator at reference level.The excitation
system of a Turbo generator contains the exciter and the
AVR. AVR acts upon DC Vf that supply excitation to the
synchronous generator.
Is This Answer Correct ? | 30 Yes | 4 No |
Answer / d oldham
The synchronous generators used do not naturally operate at
any particular voltage but the voltage can be adjusted by
manually setting the excitation. However as soon as any
load is put on the generator a different value of
excitation is required. The AVR automatically makes the
necessary adjustment by closed loop control to keep the
generator voltage constant. The operator can manually
adjust the AVR reference to allow connection to a power
system. Once connected to a large power system the AVR
setting determines the reactive power load kVAR on the
generator. A high setting exports kVAR (lagging power
factor) and a low setting imports kVAR (leading power
factor).
Is This Answer Correct ? | 7 Yes | 0 No |
Answer / mohan kumar
AVR is used to maintain the generator voltage the exciter system w.k.t the exciter give excitation to generator field wdg the the output of AVR is fed to exciter and exciter output voltage is converted to DC through RDFR and it feeds the DC volt to generator field WDG
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / raja
Any one have a book 📖 for the fundamental electrical structure of an thermal power plant.... Please send me @rajako0202@gmail.com
Is This Answer Correct ? | 0 Yes | 0 No |
what is the formulae for selcting capacitor bank to increas pf
Is MEN and RCD related to each other ?? IF yes then how??
how do you tell if a avalanche button diode is a p or an
If one lamp connects between two phases it will glow or not?
I am in last year of Engineering.I want to apply for ONGC on GATE based score.They require Certificate of Competency as Electrical Supervisor.How can i get this certificate so I can apply for AEE(ELECTRICAL) in 2016
by using pump duty, how we will can calculate the motor duty(KW)? is there any standard or formula.
I have 1500KVA transformer ,How much Maximum KW Load is allowed?
15 Answers GKC Projects Limited GKCPL,
formula for incomer breaker size calculation of powerfactor correction unit
say a transformer is designed for 33/11kv step down with ratio 0.33 for load 1 mva. if am giving 11kv as a input that same transformer what will happen to its o/p voltage. and whether it can be operated for 500kva
will there be any problem by recovering slip from single phase induction motors?
a 11 kv line is grounded and a 110 kv line is grounded. which line have the greater current flow?
what heppend if we are connected u1-v1-w1 as a star point in the place of u2-v2-w2 in power genration