What are the reason of unbalanced secondary voltage of HT
transformer 33kv/6.6kv ?
Incomming voltage is balanced.33kv each
secondary voltage 6.6 kv
6.4 kv
6.4 kv
At no load conditions.
Answer / k.prakashchandra
Probably ,inter -turn short in one phase of the primary if
delta/star .Conduct magnetic balance test (low voltage
excitation test) to ascertain.
Is This Answer Correct ? | 0 Yes | 0 No |