What is linearity of RTD over 0 to 200 degC?
Answer / dr. v.s.v.mani
0.4% of FS. The Pt 100 has 100 ohms at 0 degC, 175.8 ohms
at 200 degC. However at 100 degC, resistance is not 137.9
ohms but 138.5 ohms, which is 0.6 ohms higher. [Now 0.6/
(175.8- 100)]*100% is 0.8%. However with respect to a best
fit straight line, the deviation from straight line is +/-
0.4% of FS.
Is This Answer Correct ? | 22 Yes | 0 No |
send me HPCL paper
Which topics are covered in Process Control?
Why 1-5 vdc a standard?
1 Answers Process Control Technologies,
CONTROL VALVE OPERATING IN MANUAL BUT NOT IN MANUAL. WHAT SHOULD BE THE PROBLEM ?
why does mA signal preferred for signal transmission?
How can we calibrate pressure and flow transmitter in the field(online)?
What is BMS (Building Managment System)& is AHU / HVAC are in BMS.
why use 50% lel methane gas concentration for gas detector calibration instead of 60% lel gas concentration whereas the hi alarm set at 60% lel.
Why we are using thrust bearing at turbine side?
what is three element loop
How it the difference between force balance system and dispalacement balance system?
If we increase PI controller what will be action.