can i know how to design overcurrent setting and earth
fault for 11kv & o.433kv system assuming tx 1000kva.
Answers were Sorted based on User's Feedback
Answer / prakash.
First selected for ct ratio in HT panel.1000kva transformer full load current in primary 52.5amps.so ct ratio in 60amps(60/5).
Now relay setting for over current 55amps.
And earth fault setting 0.5amps in ct secondary amps..
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / k.prakashchandra
Normally EFR is set at 20% 0f OCR setting.
| Is This Answer Correct ? | 2 Yes | 0 No |
What is the fault or needs to be done when frequency in ac drives is not changing?
what is the affect of earth's magnetic field on the frequency used in aircraft???
what is the difference between directional & non directional earth fault with example please explain.
it says in neutral wire current flows under normal condition, but when we put tester it wont glow, why?
if the stetor speed (N S) increase by 20% then the rotor speed will be increased by 20% is it true. ?
protection used for alternator , feeder , transmission line
show the single line diagram of star delta starter with single phase preventer
what does a string of resistors in a series will do?
when we should use Central Battery system and UPS system and why? in other words, what are the differences between the two systems?
how make to Incident and accident report
What is error of a measurement?
hi i will D.E.E.E.is completed pls send rrb diploma old qustion papaer sent in my e mail. i.d.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)