What is the difference between MCCB & ACB Where it can be
used
Answers were Sorted based on User's Feedback
Answer / sujith viswanath s
MCCB-Moulded case circuit breakers ,it can be used upto 650A operating current
ACB - Air circuit breakers can be used up to 2000 A operating current
Is This Answer Correct ? | 11 Yes | 4 No |
Answer / seeni labeer
MCCB WE CAN USE 20A TO 800A, ACB WE CAN USE MORE THAN 1000A TO 4000A
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / venkat
# 9 MCCB which is nothing but moulded case circuit breaker.
ACB is nothing but Air circuit breaker and Vcb is Vaccum
circuit breaker..The main difference between last two thing
is the arc quenching medium.ACB is air circuit brekar
Is This Answer Correct ? | 0 Yes | 0 No |
WHAT IS FAULT CAPACITY OF HT MOTOR TERMINAL BLOCK? ANY BODY HAVE ANSWER PLZ....POST IT.
how to calculate the cable size for 500 kva transformer?
What is the difference between Generator Differential Relay and Transformer Differential Relay?
Why we get neutral from EB department, if not what will happen if we use earth instead of neutral? what is the result at the time of monsoon or rain with thunder and lighting ?
How earth resistance reduses by pouring water coal and salt?
Why we have use 3 & 1/2 core cable use for general electrical supply arrangement
is a normal conductor can be used a core in windings if not what is the winding core speciality.
How to improve insulation resistance of Motor
A wattmeter is marked 15 A/30A, 300V/600V and its scale is marked up to 4500 watt. When the meter is connected for 30A, 1600V, the pointer indicates 2000 watts. The actual power in the circuit in
Purpose of providing neutral isolation panel for parallel operation of diesel generator
For a Potential Transformer(PT), the primary neutral terminal must be grounded before energization. Why....? What will be heppend if we energize the PT without grounded the primary neutral point? Why..........?
if transmission voltage expressed as the multipple of form factor(1.11)........11,33,66,220 etc......then why madakkathara substation(kerala) voltage is 400kv..not 440.....?