There is 3phase power cable from 1 point to the other point
which is 100m away. Two point equipped with power meter and
recorded 1st point is 205kW while the 2nd is 202kW and each
phase average carry 400amps. To calculate the resistance of
the 3phase power cable, is the formula using will be P=I2R?
Answers were Sorted based on User's Feedback
Answer / pdbhatt69
If total loss in cable is 3 Kw hence it must be devided n
al 3 phases and hence 1 KW loss in one phase, now you can
use frmula P=I*I*R.It comes around 2.083 Milli ohm.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / shyamkr
i think the current I will be the r.m.s value of current not
he average value and P will be the power loss in the cable.
so the formula P =I(r.m.s)2 * R.then this formula will give
the resistance in the ac circuit.
Is This Answer Correct ? | 0 Yes | 1 No |
What is the suitable transmission voltage?
i am going to give the JSEB,RANCHI exam for power plant,so i need some samples of papers related to that,so please send me these papers by my mail id.
how to fit 3 HP crompton gear motor with conveyor with the use of staring delta starter or ordinary starter?
when is safety goggles use mandatory?
WHAT IS MINIMUM AMOUNT OF CURRENT THE HUMAN BEING CANT RECOVER FROM THE SHOCK,WHAT IS THE RESISTANCE OF THE HUMAN BODY
How to calculate capacitor bank size at a load 800kVA.
what is the best method of grounding in 30 MW generator?
What is NGR . What is the purpose of 10 sec ,60 sec rating of NGR.
how to select rating of HT Panel
Damping resistor provided in open delta (tartiary) winding of a measuring PT at the incoming of a MV inverter drive panel is getting heated up. Can any body explain the reasons and suggest the remedy?
is it ok to switch lights from a mcb instead of switches
what shall be no load voltage of 132/33 kV transformer ? is it 33 kv of 34.5 kV