Answer / k.prakashchandra
To dehydrate the windings.In view of high level of water /
moisture content in insulation ,it is recommended to
thoroughly dehydrate the windings by subjecting to vacuum
heating and drying after untanking the oil.Care should be
taken to see that the tank would not buckle due to the vacuum.
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / byd
Generally Hermetic Onan transnformer vaccume before oil
filteration and after oil filling,, because if there is
any air inside of transformer tank and oil then we
apply anergy after there will be short circuit and
insilation resistances will be min, and IEC 60076-1 High
voltage test, if transformer is 33kv, you should apply
mono phase to HV winding as 70kv for 1 minute,, if there
is any short circuit it means oil didnt vaccume ,, or
there is some insilation wrong ,, i am sorry my english
is not good
Is This Answer Correct ? | 2 Yes | 2 No |
how to calculate the cable size
What is “pu” in ee?
if negative of DC supply used and positive is grounded through EGB, and if ELCB used in the system then is it sense the positive volatge and get tripped is it possible?
what is meant by lagging & leading current
In Power cable specification what is U0/U and Um.
short notes on npn & pnp transisitor..........
when we design electrical schemes of 11/.415kv distribution..wen and were should we show the relays??what is the function of it?for example..we place EFR Relay CT between transformer neutral link and transformer earth.Like this what are the other type of relays we should use?why?where?Explain please..Thank you
does the power factor of an induction motor improve upon used in parallel with a synchronous condenser , used commonly to provide a leading kva ?
What will be the total current for 300kva UPS if it runs on 40 to 45 percent load. Is there any formula for to calculate the exact load.
what is safety of ups
it is possible to rotate the DG engine dc starter with wrong polarity connections? why?
difference between over current and over load protection?