Hi ,what the accurate method to set correct(In) over load to protect the 3~ motor..

Answer / pillay

I follow this method where before setting the overload
current setting I carry out an actual current consumption
test with a clamp ammeter.If the reading is lower than the
rated full load current of the motor I would set it at
actual reading add 5 percent and set it as the tripping
current. But if the the actual consumption is already the
rated fl current or almost it than the setting would be at
the rated full load current of the motor but never exceed
it.This way if it trips at any time than find out the root
cause and than only put into operation.

Is This Answer Correct ?    4 Yes 1 No

Hi ,what the accurate method to set correct(In) over load to protect the 3~ motor..

Answer / joseph

The correct setting of over load relay is 105% of full load current.

Is This Answer Correct ?    0 Yes 1 No

Hi ,what the accurate method to set correct(In) over load to protect the 3~ motor..

Answer / pundlik wanwe

For calculation of thermal over load current setting following formula is used
OLR = Motor FL current/ CT Ratio X 105%
Normally it is set at 105 %

Is This Answer Correct ?    0 Yes 1 No

Hi ,what the accurate method to set correct(In) over load to protect the 3~ motor..

Answer / simon peter

Firstly u should know the correct ampere of the load which will b drawn. According to rating buy ELCB,M.C.B of that rating .....

Is This Answer Correct ?    0 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

we have 3 single phase transformers. how will we generate 6 supply from 3 phase supply input

0 Answers   NHPC,


how to control dc motor?

0 Answers  


what is the current setting for different relay protection for transformer .

0 Answers   Crompton Greaves,


Difference between HRG and NGR. Are they both the same thing

0 Answers  


can i use 10 mfd + 6 mfd instead of 15 mfd capacitor in single phase motor as running capacitor

3 Answers  






How to calculate wire length,size & current? ( related to control panel)

0 Answers   FSS, GK Controls, Panel Tech,


Why don't we provide SURGE ARRESTORS for Transformer feeders?

5 Answers  


why diesel tank is earthed

1 Answers   ABB, NTPC,


WANTCONTACT NUMBER & EMAIL/ WEBSITE TO CONTACT THE SECRETARY,MADHYA PRADESH LICENSING BOARD(ELECTRICAL),K- BLOCK,3RD FLOOR,SATPOODA BHAWAN,BHOPAL

0 Answers  


Less cost of delta connection over star connection a. No fourth neautral wire

1 Answers  


1kva=how many kw & amps

4 Answers   Jakson,


What are PLC leader logic program method

0 Answers   AIS,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)