whycircuit breaker is not connected at the generator end
where the capacity of the generator is more say 60MW, 100MW
etc.
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
Gen side means usually 11 KV.The generator current at full
load will be very high for 60 MW( 52.5 x MVA A)for an
indoor breaker .Therefore , synchronization and tripping on
fault are done at EHT breaker which is of above 110 KV.For
any fault between the breaker and gen ,the master trip is
employed ,which trips the field breaker ,CB and the governor.
Is This Answer Correct ? | 13 Yes | 5 No |
Due to following points
1)Transient Recovery Voltage (TRV)
2)Higher X/R value
3) Delayed current Zero
circuit breakers was not used after above 60 MW generators.
However please note that now full line of IEEE C37.013
qualified medium-voltage vacuum generator circuit breakers
for voltages up to 24 kV and generators up to 200 MW for
both indoor and outdoor applications are available in
market.
Please note that Circuit breakers applied to generator
switching applications are subject to conditions quite
different than those of a normal distribution circuit
breaker used in industrial, commerical and utility systems.
Distribution circuit breakers, whether of the outdoor
substation type or of the drawout type for use in metal-
clad switchgear, conform to IEEE C37.04 (basis of ratings),
IEEE C37.06 (preferred ratings), IEEE C37.09 (testing) and
IEEE C37.10 (application.)
Is This Answer Correct ? | 5 Yes | 6 No |
define ac reactor? thier application;
What are IP protections used for electrical panels, JB, equipments installed in explosive zones like Petrochemicals, Oil & gas
what is vibration?
the grid connection required for a 50 MegaWatt fotovoltaic powerplant is higher or lower than 35kv (high or medium tension)?
What is the formula of frequency ?
how to calculate size of cable from motor current given and how to calculate full load current of a induction motor.
slor cell made?
which oil used in transformer?
Im designing APFCR Panel for 600 KVAR.I need to calculate the full current so that i can choose the capacity of isolator/Breaker.Kindly suggest with formula.
why the carbon brushes are used heat created rotating parts in eiectricity
what is load balancing. what maximum load diffence is allowed between phases.
Is HT capacitor rating connected directly to motor terminals , related to motor no load current?