what is earthed and inearthed cable or system?
Answer / mzechlin
Here is your answer:
Consider a transformer wherein the secndary of the sinding
is connected to earth or ground such that it provides a
neutral path for current flow back to the transformer. The
connection to the "Earth" or ground is considered the
Earthed connection. It provides the user the ability to
split the voltage output with reference to the legs of the
transformer. Hope that helps
Is This Answer Correct ? | 2 Yes | 4 No |
What is the value of 3 phase voltage?
how current rating of l.t cable is find
boiler is running in rankine cycle and deisel generator is....?
What is I to C?
Why the stator is rotated in ceiling fans not Rator?
Why do series motors have high starting torque?
How to convert from HP to BHP please explain????????
what is the difference between earth and neutral?
56 Answers Bhel, Emerson, HCL, JLL, L&T, Siemens, TVS,
what are the standard IR values should be of R-E, Y-E, B-E, R-Y, Y-B, B-R of VCB in closed condition and in open condition for 500KVA & 1000KVA transformers. and what is the acceptable range when tested by 5000V megger.
What are the earth resistance Standards of 66kv sub stations according to indian norms.
what is droop?
How to decide the fuse ratings for potential transformer