What do you mean by class of CTs and what is the meaning of
cl 1.0, cl5P10, cl 10P10 CTs?
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
1.0 class is for measurement 1%- error at full load.Other
two are for protection. 5% error at 10 times the rated load
and 10% ---
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / k.prakashchandra
Wrt my reply ,please correct as '5% error in measurement and
capable of taking current 10 times the rated and so on'
Is This Answer Correct ? | 0 Yes | 0 No |
actually cl is acuracy , means in what percent accuracy, cl 1, 0.5 is for metring purpose , and cl 5p 10 , ps , 10p10 is all for protection means for relay out put , means 5 % accuracy and 10 % accuracy
Is This Answer Correct ? | 0 Yes | 2 No |
we all know that both the generator and motor are electromechanical conversion devices.....then why we rate motor in kw and generator in kva????
I have a generator of 300kw.400V,50hz . what is means can i assume the load Red Phase with Neutral 300kw.Yellow phase with neutral 300kw and Blue with neutral also 300Kw. or - red with neutral 100kw same as yelloe and blue phase also giving 100kw with neutral respectively
HOW DISTANCE PROTECTION IS DONE IN EHV TRANSMISSION LINES? WHAT IS THE BASIC TECHNIQ OR FUNDA USED BEHIND THIS ? SPECIALLY EXPLAIN?IMPEDANCE METHOD.
what is the minimum dielectric stregth of transformer oil.
differnce between single acting and double acting solenoid valves
What type of wiring series or parallel is used for conventional and addressable type FAS & why?
how to compute kAIC? with formulas...
Stator of 3-phase IM has 3 slots per pole per phase. If supply frequency is 50 Hz, calculate the speed of rotating stator flux A 1000 rpm B 500 rpm C 1500 rpm D 1440 rpm
How impulse levels are calculated that for 11kV impulse is 75kvp, for 24kV impulse is 125kvp ?
why the neutral point of star connnection oscillates?
i completed my b.tee(eee) in 2009, but i did not join any job, i joined in my father business, now i want to join any good job, please suggest any course for me
Sir if i have 2kv ups in which 17ah 8 battries load 600watts how much back up time i get and if i put 6kv ups with the same no of battries same amp can i get more back up time please give reply exactly what is the procedure to calculate back up time for different kv,s