1)why the transformer rating in KVA insted of KW
2)why the secondary of ct is shorted and why the PT
secondary is open
Answers were Sorted based on User's Feedback
Answer / vinod
1) The Efficiency of the transformer depends on copper
loss and core loss, prepotional to the voltage & square
ampere.also power factor is depend on load. thats why
transformer is rated in KVA.
2) CT secondary is either connected with relay/ICT or it
will be shorted as it is working as step up voltage
(dangerously high) principle, cause human/equipment damage
PT is using as a voltage measurement and
protection,winding must be open or connected with load of
rated burden.
Is This Answer Correct ? | 8 Yes | 3 No |
Answer / guest
when open circuit test of transformer we will got the iron
loss it will depends upon voltage and during short circuit
test we will got the copper loss it will depend upon
current there fore total loss in VA so we use large
capacity of transormer hencetransformer capacityis in KVA.
2)if ct secondary is open heavy emf will produced so
sarrounding equepement will burntout and CT willalso burnt
or saturated.
Is This Answer Correct ? | 4 Yes | 6 No |
Answer / venkat
we dont know transformer manufacters the load power factor
cosumer so the trasformer rating in KVA
Is This Answer Correct ? | 0 Yes | 2 No |
Is there chopping current in resistive circuit
We have ONLINE UPS 15KvA (3PHASE 440V I/P,3PHASE O/P,440V) I want to step down from 440 to 220 V What to do. Pl. suggest with specification.
why we calculate only 11kv 33kv and 132kv ... why not 10kv 20kv 45kv?
what is the difference between megger and earth tester?
28 Answers Ashok Leyland, IOCL, RRL,
sir i am apearing for nic exam.i dont know exam pattern.can you please send me some model papers
One of our gas turbine generator unit "1st stage rotor ground fault" alarm was occured several times. we tried to measure some voltage vulue ground fault protection relay (UNS3020a made by ABB and we measured the value of: Ground: 0.9VDC 5V: 5.8VDC 24V: 23VDC u+: 300 – 350mVAC Rf1: 17.5mVAC Rf2: 17.6mVAC The unit still running and the alarm was reset. As of 6pm yesterday and unitl now no alarm happened again. I our protection relay was defective?
what is load which is indicated in power plant generation panel? in any power plant
what is the current rating of 2500 KVA,33KV/433v transformer on secondary(LT) side
9 Answers Reddy Labs, Vitrum Glass,
what is p.s impedance measurement test in earthing transformer?
draw single line diagram of UPS
1 Answers Adani Ports, Equate, IBM, SAP Labs, Socomec, TATA,
why dc power can not be used in transformer?
33 Answers GE, Sail,
HOW TO CALCULATE EACH PHASE CURRENT WHILE A MOTOR CONNECTED TO STAR- DELTA STARTER?