in a refinery one motor is suddenly stoped. what
will do
how can i findout the problem explain step by step
Answers were Sorted based on User's Feedback
Answer / bhavesh n r
First of all pls ensure that if overload relay is tripped or
not.then check motor winding resistance & insulation
resistance of winding with body.then check motor shoud
rotate freely without jerk.if u any query then pls mail me @
aundal.bhavesh@yahoo.com
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / shivakumar
Control wiring also problem, interlock working are not working,when feed are not com feeder automatically stopped
Is This Answer Correct ? | 0 Yes | 0 No |