could i arrange a faulty and healthey battery bank togather
in parallel , if your ans is not then why?
Answers were Sorted based on User's Feedback
Answer / pillay
the good battery bank will be discharged by the faulty battery bank.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / abhishek goyal
No because faulty battery bank both rod or plates are melt
we also called it might be short. so if we connect the
faulty battery bank into parallel connection with healthy
battery it will be discharge through the faulty battery.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / jayanta dutta
No we could not arraneg a faulty and a healthey battery bank togather in a parallel. Because it consume more energy but backup remain the same. Result energy lost.
| Is This Answer Correct ? | 1 Yes | 3 No |
we erected (48HP)63kva dist transformer and incoming from 11kv line,out going is 415v domastic line 2.04 km.for that actual output current is 84A. what are the losses and final output current.
What is the typical enclosure type used for Indoor switchgear / Outdoor switchgear Units? - In Onshore / offshore Units?
to hook up ten 50 amp rv pedastels at a lenth of 600 feet from the service what size will my service need to be and the size of wire will I have to run to each pedastel in series??????
What is the use of Isolation Transformer, and Neutral is using for return path, finally this current is going.... but same time the voltage of the neutral should be below 1 V...
How to calculate the multiplying factor for energy meter with ct ratio given
what is active network?
Why no-load primary current is very small as compared to full load current in transformer (as 1% of full load current?
how the frequency was generated in power station
neutral carrying current more than phase in 3phase supply.i want to know the reason?
What is the difference between Relay and Contactor
my self i am raghu working as tech.. in my college the maximum demand is 211 kva presently we are using 12kva capacitors the target power factor is .95 so what capacity of capacitor banks should i install
The ratio of white balls and black balls is 1:2. If 9 gray balls is added it becomes 2:4:3. Then what is number of black balls ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)