WHAT IS SITTING AMPS IN OVER-LOAD RELAY FOR 1PH OR 3PH
MOTORS?IF ITS NAME PLATE GIVEN MAX AMPS 10AMPS?
Answer / k.prakashchandra
The overload relay may be set at 110-120 % of the rated
current of the motor
Is This Answer Correct ? | 3 Yes | 1 No |