formula for incomer breaker size calculation of powerfactor
correction unit

Answers were Sorted based on User's Feedback



formula for incomer breaker size calculation of powerfactor correction unit..

Answer / nur.asidik

you need to consider of breaking capacity too

Is This Answer Correct ?    2 Yes 0 No

formula for incomer breaker size calculation of powerfactor correction unit..

Answer / matt

Given a system power factor of 0.9, PFC unit of 50kvar we can work out the following

50/0.9 = 56 A real current

56^2 * 50^2 = 75 A apparent current

Cable capacity - 75 * 1.35 = 100 A

Factor of 1.35 used for over rated capacitors as per
industry standards.

Breaker shall be rated at less than the cable capacity but greater than 75A. Increase cable size to suit breaker breaker sizing if required.

Is This Answer Correct ?    6 Yes 6 No

formula for incomer breaker size calculation of powerfactor correction unit..

Answer / mohan

Amps Per KVAR is between 1.1 to 1.3 Amps

for a 300KVAR panel

the current shall be 130 AMPs(and if the capacitors are
auto swithced , then switching surges need to be considered
hence) * 1.5 Times = 585Amps
The nearest breaker size is 630AMPS

It is preferable to use Capcitor duty contactor for
switching

Is This Answer Correct ?    1 Yes 6 No

Post New Answer

More Electrical Engineering Interview Questions

what is load which is indicated in power plant generation panel? in any power plant

1 Answers  


hi pot test principal

1 Answers   NTPC,


in star connected 4wired transmission system ,what happen if the neutral is grounded . or not grounded. which is significant and y

2 Answers  


at work we have a 3 phase motor but on testing one phase isnt getting a reading. it runs 24 hours a day all week. stops and starts well no noise or heating. the phase isnt down to earth.is it just a bad meter reading or not? phases one and three came up with a resistance reading of 0.4 but phase 2 couldnt get anything shows up as open circuit.

0 Answers   iGas,


types of motor starter

5 Answers  






how rectifier transformer work in electroststic precipetatore(esp?

0 Answers  


I want to know all basics of electrical engineering

0 Answers   RRB,


What is the basic difference among IPS,UPS,EPS?

2 Answers   ABB, Navana,


WHY MOSTLY Rph IS USED FOR CONTROL CIRCUITS AUX. SUPPLY ?

0 Answers   UltraTech,


Why the CT Secondary is rated as 5A generally?

2 Answers  


can any one provide some material?

1 Answers  


in parallel operation of power transformer why the distance between power transformer and capacitor bank feeder is necessary to know

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)