If a differential pressure transmitter is calibrated for
0~2500 mmH2o and transmits a 4~20mA dc signal. The
transmitter is placed across an orifice plate which is sized
to create 2500 mmH2o differential at 5000m3/Hr
a) what is the flow rate when the transmitter signal is
13.0mA DC?
b) what is the signal output of the transmitter when flow
rate is 2500 m3/Hr ?
Answers were Sorted based on User's Feedback
Answer / nani babu
a) flow rate for 13mA is 2812.5 m3/hr
b) 12 mA to 2500 m3/hr
Is This Answer Correct ? | 24 Yes | 6 No |
Answer / nabil amrani
a) Y=(20-4)/(5000-0)*x + b=16/5000*x + 4
when y = 13 mA x = (13-4)* 5000/12 = 2812.5 m3/Hr
b) Y=16/5000 * x + 4
when x= 2500 y= 16/5000 * 2500 +4 = 12 mA
Is This Answer Correct ? | 8 Yes | 3 No |
Answer / raju
ans a)=√(13-4/16)×5000=3750 m3/hr
b)=(2500/5000)×(2500/5000)×16+4= 8 mA
Is This Answer Correct ? | 13 Yes | 13 No |
what is the meaning of Domain server?
What is electronics?
Describe how to calibrate various types of instruments and transmitters using ISA industrial consensus standard techniques.
who discoverd ohms law?
What is the difference between compensation and extension cable.
I have a steam flow DP transmitter that has output swinging. Steam valve is in manual.I have good steam pressure. The impulse lines have steam tracing on them. The steam tracing has a hole in it that is blowing raw steam on the high side impulse line only. Could this be causing the swinging?
1 How to calculate dp transmitter steam and water? 2 impulse line for liquid steam and gas
1 Answers Sitara Chemical Industries,
What is Hysteresis mean in Instrument?
What are three main programming in PLC
what is dedband in instrumentation ?
What is the logic a Transmitter control a Control Valve? How the signal going to the Control valve? What are systems/Panels/cables/signal used to control valve from Transmitter?
Can we place a Control Panel in Hazardous area Group IIC ? If 'yes' then is there any approval required? If 'yes' then there is any specific IP rating or any standard required? If 'Yes' What is MOC of control panel?