Dear Friends,
I have a 500KVA transformer supplying whole factory having
3 phase and single phase mixed loads. Power room has
ammeters connected via CTs for individual phase. Now I know
that readings shown on meter for each phase say R,Y and B
are line currents. But when I want to know the total on
transformer do I need to add the currents of all three
phases readings shown on meter or value for anyone phase
will give me the correct power load on transformer for that
point of time.
2. If ammeter shows unbalanced readings for R,Y, B phases
say 150, 250 and 300 respectively so can I assume that 150A
i.e average of 3 will be the 3phase load currents and
remaining will be 1phase currents. Please clarify my doubt.
Answers were Sorted based on User's Feedback
Answer / ahmadmukhtiar
1. The load of R, Y or B will be the total load on
transformer.
2. There must be phase balancing system for protection
otherwise the equipment connected as load will get damaged
if all three phases are unequal.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / k.prakashchandra
Calculate load(KVA) on each phase and add
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / sakthivel
each phase you find consuming power with use ammeter reading
and volt meter reading
each phase you regulate the load current or equal load
current load you choose
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / abdul karim
If you wants to know the total load of transformer , you must use a watt metrer , OR you will calculate the load in watts of every individual phase then sum of all three phases will be your answer.
| Is This Answer Correct ? | 0 Yes | 1 No |
Why the CT Secondary is rated as 5A generally?
Is it possible we are step down 11 kv to 230v ?
What is DC series motor?
in elevator industries , how to calculate the required KVA for the elevator (elevator spec- 40A module , motor of 13.5KW, 20A)
1 Answers DLF, Tata Steel Limited,
what is invertor supply and raw powersupply
Why alternators are designed at 0.8 pf lag?
why we use to transmit the power in three phases intead of single phase ?
We have 2 11kv/433v transformers for 2saperate acb for mv panels and 1 bus coupler acb. Suppose I’ll close bus coupler what will happen or it will be share the load. Please suggestion and any modification required.
PLEASE TELL ME ABOUT QUESTION PAPER OF UPCL ENTERENCE EXAM.
how i define power factor when some one ask me ,,,,,what is power factor ,,,,,pleas define it simple. (pleas dont use these worlds ,,the difrence bitween apparent power and actual power is power facter )
whati s the sludge current in ups
kva/kvr
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)