generator(Deutz 550kv)is runing for 2 hours with load of
900 amp and then it goes in shutdown with alarm fault
messege of speed fault although heirtz reading fixed at
50,what does that mean
Answer / k.prakashchandra
Gen voltage can not be 550 KV which I think ,is the tr
voltage. Hz is at 50 even after gen has tripped.That
means ,it was connected to grid.The gen might have tripped
on over speed due to load throw-off. If not, speed sensor
of the gen is to be checked
| Is This Answer Correct ? | 0 Yes | 0 No |
what is impedence (Z) of transformer, what indicate in transformer , which perameter indicate in transformer
is there any difference in reading or error in value, if we connect the R phase in Y terminal and Y phase in R terminal of electronic energy meter of 11 kv feerders???
What is the meaning of TRI Vector meter?
7 Answers ABB, Excel Power Switchgear,
how to check three phase motor torque value?
how encoder works?
why most of junction box vendors providing T5/T6 Temp class jb's for T3 area any special reason?
what size steel armoured cable is required to support 1500kva capacity. would 70mm squared be enough or would I need 90 or 120mm squared 3c plus earth
374kvar capacitor bank connected across 600kw,6.6kv motor.what will happen if motor run at 50% , whether full kvar applied or half?
in how many ways we can make induction motor to run in reverse direction?
what are adantages of OC and SC test over the load test?
What is Skin effect in Cable?
what is two wattmeter test
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)