Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


Why hunting will occour in control valve?

Answers were Sorted based on User's Feedback



Why hunting will occour in control valve?..

Answer / s vedpathak

Control valve is used in close loop control system.If it is
hunting , then to troublshoot first put loop for few sec in
manual mode, still if v/v is hunting then it is field
problem i.e v/v or I/P converter problem.

If it is not hunting in manual mode, then the problem can
be either the loop process variable(PV) is hunting or if PV
is ok, either the load/process is varied or loop needs
tuning.

Is This Answer Correct ?    57 Yes 1 No

Why hunting will occour in control valve?..

Answer / kumar

1)I/P PROBLEM
2)INSTRUMENT AIR LEAK(Signal)
4)FLOW DISCHARGE FROM THE PUMP MAY FLUCTUATING.

Is This Answer Correct ?    15 Yes 2 No

Why hunting will occour in control valve?..

Answer / mahesh kumar

Hunting Occur in theControl Valves due to inproper tuning
of PID loop, to remove thr hunting & for smooth operation
Tune the PID loop by adjusting the Gains

Is This Answer Correct ?    17 Yes 7 No

Why hunting will occour in control valve?..

Answer / sam.r

An undesirable oscillation of appreciable magnitude,
prolonged after external stimuli disappear. hunting is the
evidence of operation at or near the stability limit.

in control valves is caused by the oscillation in the
loading pressure to the actuator caused by the instability
in the control system or the valve positioner .

Is This Answer Correct ?    5 Yes 2 No

Why hunting will occour in control valve?..

Answer / sujitkumarnaik@indiatimes

if there is haunting in c/v that means there is disturbance
in i/p signal & o/p signal or feed back.so firstly calibate
it n observe.if still same prob. coming,adjust the pid tunning.

Is This Answer Correct ?    4 Yes 3 No

Why hunting will occour in control valve?..

Answer / mostafa abo el-kasem

Several reasons can cause valve hunting; it can be from signal or from hard ware
To define:
1- Check controller o/p is stable while valve “you can put it in manual mode” is hunting or not (if not stable then it could be from the configuration or from PV change, you can check transmitter/damping/configuration,)
2- If signal is ok ,then it will be hardware problem from
a. Feedback arm not fixed
b. I/P problem
c. Diaphragm damage
d. Flow irregularities
e. Positioner tuning

Is This Answer Correct ?    1 Yes 0 No

Post New Answer

More Instrumentation Interview Questions

Where are oxygen analysers installed in cfbc boilers? What are their usual readings?

0 Answers  


how to calibrate Necleuonic level transmitter.?

0 Answers  


What is the use of valve positioner?

1 Answers   CCIE,


Which softwere is required to communicate the S7-300 processor

4 Answers  


what happen if i install my pressure transmitter below the elevation of pipe in natural gas service. Also support your answer

3 Answers   C2C,


How to Calibrate Ultrasonic Level Transmitter in field

0 Answers  


What is stripper & spilitter ? Diffrence in this.?

0 Answers   JSW,


i have done DAE in Instrumentation and Process Control. i have applied for an apprentice training in chemical company after three day my interview will be conduct but i need more information about industrial process control and controller. my e mail is imran_dilsetu@yahoo.com please tell me interview question relative to instrumentation ?

0 Answers  


what is diffrence between analog card and digital card in plc.how analog card work,Please explain in detail.Please send it on abhi_vyas@sify.com

6 Answers  


any one suggest me how to calculate percentage of air leakage with formula,

0 Answers   SSL,


how do we commission inergen system?

0 Answers  


In 2 wire transmitter 1 wire is used for power and other is used for signal( 4-20)ma In 4 wire transmitter 2 wires are used for power and 2 wires are used for signal (4-20)ma . but my question is "what is the criteria or parameters we have to consider while selecting these transmitters for eg( distance, safety zones etc.

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)