what is the difference between Resin Cast CT and Oil cooled
CT?
Resin Cast CT and PTs are usually used in indoor
switchgeear 11kv or 6.6kv substations etc. whereas Oil
cooled CTs are used in outdoor substations viz 11kv or 33kv
switchyards.
Difference is that Resin cast are solid cast type. Oil
cooled are those immeresed in Transformer oil and sealed.
In larger capacity CTs where cooling is required then oil
cooled CTs are preferred.
Is This Answer Correct ? | 10 Yes | 0 No |
3 Core x 35 Sqmm Cable (How we measure 35Sqmm)
4 Answers Alpha Star, Brother,
What happens when ac supply is given as excitation voltage instead of dc supply
what is the per unit cost of generation of electricity at thermal,hydro,desael,solar,gas power plant
why transformer ratings in kva? & DG ratings in kva? & Motor ratings in kw/HP?
how much earth resistance consider to commissioning the transformer?
what is the reason for harmonics introduced in the line
Can we use a window type neutral CT instead of a bar type neutral CT. We have an issue with a neutral bar type CT of 800/1 ratio with a Circuit breaker NS800L shneider type, and we want to change it with a window type. Pls advise. Thanks
i want to measure voltage difference between neutral and earth so i just simply use voltmeter. my question is that may i use this measure continuosly.or there are some electricity board restrication on that? or it creat some problem on my measuring device..?
What is the SPEED of electricity?
WHY TRANSFORMERS ARE RATED IN 11KV 22KV 33KV Instead off 10kv 20kv 30kv
If the positive terminal of batteries in 125 v dc system is connected to earth what will happen ?
how much allowable resistance that can be difference in motor all coils?