What are the testing to be done before the installation of
1000 KVA Transformer?
Answers were Sorted based on User's Feedback
Answer / jyotirmaya
Normally test are done before installation and commissioning
of the transformer. The following test are done;
1. Visual Inspection
2. Insulation Resistance Test
3. Ratio Test
4. Vector Group Test
5. Magnetizing Current Test
6. Core Balance Test
7. Winding Resistance Test
Is This Answer Correct ? | 38 Yes | 3 No |
Polarity Test also an important before loading
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / rajan singh tanwar(j.k. cement
For Power
Transformers the
following Pre
Commisioning tests
are done:-
1.Visual Inspection
2.Measurement of IR
Value
3.Measurement of P
I Value
4.Measurement of
Winding
Resistance
5.Short Circuit Test
6.Oprn Circuit Test
7.Magnetic Core
balance Test
8.Voltage Radio Test
9.Oil BDV & Acidity
Test
10.Checking the
function of
OTI, WTI, OSR, MOG,
PRV
Relays
Last one for the
relay's testing but
it also comes under
transformer testing.
Thanks
Is This Answer Correct ? | 3 Yes | 0 No |
what is load cell
what is the meaning of knee point in current transformer and how to calculate?
What do you mean by class of CTs and what is the meaning of cl 1.0, cl5P10, cl 10P10 CTs?
what is inverter and converter
7 Answers Shrishti Power Technologies,
why the check zone and main zone are used for Busbar Protn. scheem?
what is the formula for converting dc power(watt) to ac power (watt)?
why resistive load has unity power factor,inductive load lagging and capacitive load leading power factor?
what is saturation in transformer
Can a transformer be used as voltage or current amplifier?
How does solar power system work?
How to calculate CT ratio for 11KV 1500KVA Transformer 500KVA MD and 1400KVA connected load ? Note:- As per MSEB(Maharastra state electricity Board)
what will be happen if we apply D.C supply to the transformer