DG's are usually rated at 0.8 PF lagging. There is no
issues with running the DG at another higher or lower
lagging PF. Usually the output kw of the engine is set at
80% of the kva rating. For example a 100 kva DG will have
an engine rated at 80 kw. This will al;low for a full load
current of about 140 amps at 0.8 PF. Increasing the PF
towards unity the maximum load current must be reduced
until it is about 110 amps otherwise the engine will be
overloaded. If the PF is reduced below 0.8 PF the maximum
current must not exceed 140 amps. This means the kw of the
load must be reduced. This is to stop the windings in the
alternator being burnt.
Going to a leading PF will cause voltage instability and
can cause damage to the alternator.
| Is This Answer Correct ? | 1 Yes | 0 No |
Keeping pf at 0.8 lag when running in parallel means the
terminal voltage of gen is higher than the system or busbar
voltage.But it results in higher gen & field currents which
cause unwanted heating of armature and also the field.If
you keep the pf at unity or -ve,the gen does not contribute
to system stability.The generator should also share the
reactive power of the system, which is usually
lagging.Anyway pf may be maintained at 0.9 to 0.95 lag.
| Is This Answer Correct ? | 0 Yes | 1 No |
I have a relay contact rated at 220v dc which is supplied with a 24vdc from the panel,for it to trip the dampers(24vdc).What if the application of the relay changes so that it should work at its rated 220vdc then will it work at 24vdc supply given or any other consideration needs to be taken .....
Which factor decide the colour of the light emitted from a Led?
How to select busbar?
In winding design, the angle of chording (β) is nearly equal to A 45 degree B 60 degree C 30 degree D 90 degree
A circuit breaker on detecting fault will a. Open b. Close c. Open and trigger the alarm
What will hapen if we run generator below 47.6hz frequency?
Why the Transformer connection is changing in different transformer?(Like Star & Delta,Delta & Delta,Star & Star,Delta Star) From that connection where it is used?
Why a dc generator gives result during two different condition,- 1)separately exited gen.- Eg=110 V, field current=0.25 A. 2) self exited gen.- Eg=30 V, field current=0.025 A.
on which power factor synchronous motor run
what is the electrical?
Find the netid and hostid for the following classful IP addresses? i) 117.34.3.8 ii) 132.57.8.6 iii) 207.3.54.12
MCB is used for high rating &MCB is used for lower rating.What is technical difference between ACB & MCB?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)