What will hapen if we run generator below 47.6hz frequency?

Answers were Sorted based on User's Feedback



What will hapen if we run generator below 47.6hz frequency?..

Answer / manoj sharma

Actually in india our all power system equipments are
designed to operate at 50 HZ. at lower frequency
performance of these component is poor in view of power,
life of equipment and safety. Motors will run slower,
transformers output will reduce, harmonics will increase in
power system. second thing when you run generator at
47.6HZ, your generator will loss its synchronism with the
grid.

Is This Answer Correct ?    52 Yes 2 No

What will hapen if we run generator below 47.6hz frequency?..

Answer / a.mishra

According to Alternator voltage eqn., MAX.FLUX is inversly
proportional to FREQUENCY. If we reduce the frequency,then
max. flux will increase and the problem of core saturation
may happen. Other problem of iron losses will increase in
that alternator as well as the system equipments connected
to that source like Transformers,induction motors.

Is This Answer Correct ?    9 Yes 1 No

What will hapen if we run generator below 47.6hz frequency?..

Answer / chandru williams

since all the equipments are designed to run at a frequency
of 50 Hz ( +/- 2 Hz) , low freuency will make the generator
to run at a speed less than the designed value thus
hindering the designed value of output.

Is This Answer Correct ?    8 Yes 5 No

What will hapen if we run generator below 47.6hz frequency?..

Answer / vimal dixit

Generator will go out from synchronizm with grid.

Is This Answer Correct ?    5 Yes 3 No

What will hapen if we run generator below 47.6hz frequency?..

Answer / piyush maghnani

A sthe generator frq reduced the inductive load will draw
high current which will result in poor power regulation.
the motors will not be running with standard speeds. there
will be increase in harmonics disturbances. your generator
will be overloaded & loose synchronisation with grid supply.

Is This Answer Correct ?    2 Yes 1 No

What will hapen if we run generator below 47.6hz frequency?..

Answer / gunasekaran

turbine blade will be damaged frequency variation in india
only +-3% only.

Is This Answer Correct ?    2 Yes 2 No

What will hapen if we run generator below 47.6hz frequency?..

Answer / vivekanand

Hi, do any legal standard for frequency tolerance
recommendation is there for the diesel fueled genset?
Do special criteria for frequency tolerance based on loading
is mentioned in any legal standard?

Is This Answer Correct ?    0 Yes 0 No

What will hapen if we run generator below 47.6hz frequency?..

Answer / rahul

Nothing will happen because we can operate a frequency + or- 5%.

Is This Answer Correct ?    0 Yes 5 No

What will hapen if we run generator below 47.6hz frequency?..

Answer / praveen420

In india we can't get power frequency less than 48.5hz.
Below this frequency power system violate.
If we run motor below this range than motor coil will be
burn due to more losses.

Is This Answer Correct ?    6 Yes 25 No

Post New Answer

More Electrical Engineering Interview Questions

what is meant by class 1 E in electrical power supply?

0 Answers  


What is an Automatic Voltage Regultor & what is its use? What are the general componets we use to design an Automatic Voltage Regulator..What are the factors to be considered for its design?

3 Answers  


if field winding of synchronous generator are shorted on each other will it start or burn or run for short time like induction motor

1 Answers  


I WANT YHE TECHNICAL AND ELECTRICAL SPECIFICATIONS OF 2x4MW 11KV 2x10MW 11KV 2x25MW 11KV 2x100MW 11KV HYDEL POWER PLANT i.e PROTECTION SYSTEM,MONITORING,CONTROL SYSTEM,GENERATION,SYNCHRONISATION,METERING PLEASE SEND THE DETAILS TO MY MAIL ID SPRAVEEN_222@YAHOO.CO.IN

0 Answers  


How to test Alternator stability test for REF relay

0 Answers   Amprotec,






sigal phase supply is 230 v ac two phase supply is 415 v ac then why three phase supply having supply is 415 v ac why not 690v ac

2 Answers  


In CT's they mentioned 400/5 or 1250/5, 1000/1 here 400,1250,1000 is Breaker Capacity what is the /5 Explain me briefly

2 Answers  


why transmission line 11Kv OR 33KV,66Kv not in 10kv 20kv?

43 Answers   A2Z Group, Baiji Power Plant Gas, Electrical, HCL, Kirloskar, Mepco, NEPC, OAMC, UNI, University of Lahore,


The unit of quantity of electricity is the:(a) volt(b) coulomb(c) ohm(d) joule

1 Answers  


How to calculate the cross section area for a 350 m cable, motor power is 26 kw???

1 Answers   Orient,


what is the difference between Ith & Iu rating in MCCB. Particularly on SACE ABB Circuit Breaker?

2 Answers   Siemens,


If we have 11 kv RYB Phase single core cable near about. Then wht effect and losses

0 Answers   Kirloskar,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)