CT is used for measuring high currents. even in a circuit
breaker it is used to measure the current and to send the
signal to the relay in case of any abnormality.
the 400/5 on the CT denotes the transformer ratio. that is
when 400Amps flows through the primary of the CT the
secondary of the CT is induced with 5Amps, which is easy
for measurement.
so the fraction on the CT denotes its ration which defines
the value of current flowing in the secondary side.
Is This Answer Correct ? | 17 Yes | 2 No |
what is gapless metal oxide techniques?
What is meant by Load Encroachment in OHL Feeder Protection?
what happens when ac supply is given to the dc motor and dc supply is given to the ac motor?
what are the dimensions for 200 kva transformer plinth (plateform),in which pcc m20 is used..
how can u do the earthing of an aeroplane?
One B.O.T Unit ??
What is difference between safe PLC and normal PLC
IF we have three 30KW motor, these motors are connected in DOL, star-delta and VFD respectively, what will be the fuse rating for the above three?
I have a shop heater with a 1/3 hp capacitor start, induction motor driving the fan. Intermittently, the fan motor speeds up significantly for several seconds (15-60 sec) then slows to normal operating speed. The manufacturer suggested changing the capacitor which made no sense, but I did it to no avail. Could this possibly be caused by the centrifugal switch intermittently reconnecting the start winding?
Why indicate only 440V to 3-phase supply.
star delta advantage and disadvantage?
can we produce cosine wave instead of sine wave? will it usefull?