How to calculate the Airconditioner capacity for a standard
telecom BTS shelter?
Answers were Sorted based on User's Feedback
Answer / gajanan bharad
I am too seeking right answer, but I know that the calculations above are incorrect. We have to consider the heat generated by BTSs and not the power consumed by BTSs. We have to take into account the heat generated/ rate of heat generation in Watts by all the equipment inside the shelter. There are 48V SMPS, Battery sets, BTSs, Microwave equipment, lights and assume 2 persons working. Heat generated by the SMPS equals input power minus the output power (i.e. loss of energy in terms of heat). But for rest items need the information on heat generated. Then only we can arrive at correct air conditioner capacity requirement.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / suraj.dahiya
Genarally 1 Ton capacity means---The cooling produced by
melting of 1 ton of ice in a day is.taken as unit of
refrigeration (in tons). Now unit of refrigeration used in
S.I. System is KW. 1 ton of refrigeration = mass of ice x
latent heat of ice / 24 hrs i.e
= 900 kg x 335 KJ/Kg ( one short ton = 900 kgs )
---------------------
24 x 3600 secs
= 3.4895 KJ/Sec Now we should convert KJ to KW i.e 1KJ=1KW
so 3.5 KJ / Sec = 3.5 KW
that is 1 ton of refrigeration = 3.5 KW
Always in telecom sheleters we shold take the load of BTS
For Ex: In shelter there are 4Nos of BTS,If each BTS is
consuming 20A the total Amps for 4BTS is 80A.
So The total Load of the BTS is P=VI i.e
P=230*80=18400Watts i.e 18.4KW Now each 1Ton =3.5KW we can
suggest for 5Ton of AC for 18.4 KW
plus surface area of BTS shelter suppose (9feet*6 feet)=54
sqft area.
required temp =54*25=1.350 kw
so total kw = 18.4+1.350=19.7KW
total Tr. required to cool the shelter @25 C =19.7/3.5
=5.6 Tr. AC required
| Is This Answer Correct ? | 2 Yes | 5 No |
Answer / chandrashekar
Genarally 1 Ton capacity means---The cooling produced by
melting of 1 ton of ice in a day is.taken as unit of
refrigeration (in tons). Now unit of refrigeration used in
S.I. System is KW. 1 ton of refrigeration = mass of ice x
latent heat of ice / 24 hrs i.e
= 900 kg x 335 KJ/Kg ( one short ton = 900 kgs )
---------------------
24 x 3600 secs
= 3.4895 KJ/Sec Now we should convert KJ to KW i.e 1KJ=1KW
so 3.5 KJ / Sec = 3.5 KW
that is 1 ton of refrigeration = 3.5 KW
Always in telecom sheleters we shold take the load of BTS
For Ex: In shelter there are 4Nos of BTS,If each BTS is
consuming 20A the total Amps for 4BTS is 80A.
So The total Load of the BTS is P=VI i.e
P=230*80=18400Watts i.e 18.4KW Now each 1Ton =3.5KW we can
suggest for 5Ton of AC for 18.4 KW
| Is This Answer Correct ? | 3 Yes | 9 No |
What is the necessary condition for stability.
how to calculate energy meter multipling factor by ct & pt raitio
How out of step protection relay works?
can u tell the difference between star - star transformer and delta to delta transformer?
what is the diffrence between kav and kvar?
what is the difference b/c choke and ballast?
Is it possible to control the power in transmission lines by remote controlling method?? if yes explain in details???
if field breaker of generator is closed prior to its rated speed on a power generating unit. what will be the effect on generator, unit transformer and starting transformer.
why extension in transmission tower is made?
why use celling fan wing is two or three ?
The insulation resistance of a cable can be measured by
if the power factor is .88 i want to increase the power factor to .99 what number of capacitor is to add?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)