How to calculate the Airconditioner capacity for a standard
telecom BTS shelter?
Answers were Sorted based on User's Feedback
Answer / gajanan bharad
I am too seeking right answer, but I know that the calculations above are incorrect. We have to consider the heat generated by BTSs and not the power consumed by BTSs. We have to take into account the heat generated/ rate of heat generation in Watts by all the equipment inside the shelter. There are 48V SMPS, Battery sets, BTSs, Microwave equipment, lights and assume 2 persons working. Heat generated by the SMPS equals input power minus the output power (i.e. loss of energy in terms of heat). But for rest items need the information on heat generated. Then only we can arrive at correct air conditioner capacity requirement.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / suraj.dahiya
Genarally 1 Ton capacity means---The cooling produced by
melting of 1 ton of ice in a day is.taken as unit of
refrigeration (in tons). Now unit of refrigeration used in
S.I. System is KW. 1 ton of refrigeration = mass of ice x
latent heat of ice / 24 hrs i.e
= 900 kg x 335 KJ/Kg ( one short ton = 900 kgs )
---------------------
24 x 3600 secs
= 3.4895 KJ/Sec Now we should convert KJ to KW i.e 1KJ=1KW
so 3.5 KJ / Sec = 3.5 KW
that is 1 ton of refrigeration = 3.5 KW
Always in telecom sheleters we shold take the load of BTS
For Ex: In shelter there are 4Nos of BTS,If each BTS is
consuming 20A the total Amps for 4BTS is 80A.
So The total Load of the BTS is P=VI i.e
P=230*80=18400Watts i.e 18.4KW Now each 1Ton =3.5KW we can
suggest for 5Ton of AC for 18.4 KW
plus surface area of BTS shelter suppose (9feet*6 feet)=54
sqft area.
required temp =54*25=1.350 kw
so total kw = 18.4+1.350=19.7KW
total Tr. required to cool the shelter @25 C =19.7/3.5
=5.6 Tr. AC required
Is This Answer Correct ? | 2 Yes | 5 No |
Answer / chandrashekar
Genarally 1 Ton capacity means---The cooling produced by
melting of 1 ton of ice in a day is.taken as unit of
refrigeration (in tons). Now unit of refrigeration used in
S.I. System is KW. 1 ton of refrigeration = mass of ice x
latent heat of ice / 24 hrs i.e
= 900 kg x 335 KJ/Kg ( one short ton = 900 kgs )
---------------------
24 x 3600 secs
= 3.4895 KJ/Sec Now we should convert KJ to KW i.e 1KJ=1KW
so 3.5 KJ / Sec = 3.5 KW
that is 1 ton of refrigeration = 3.5 KW
Always in telecom sheleters we shold take the load of BTS
For Ex: In shelter there are 4Nos of BTS,If each BTS is
consuming 20A the total Amps for 4BTS is 80A.
So The total Load of the BTS is P=VI i.e
P=230*80=18400Watts i.e 18.4KW Now each 1Ton =3.5KW we can
suggest for 5Ton of AC for 18.4 KW
Is This Answer Correct ? | 3 Yes | 9 No |
what are safety seals in HT line?
What is the function of pulse transformer?
When Neutral exceeds or equals the phase current in both single phase * three phase system?
Why we use two wattmeter during block rotor test and no load test of 3phase induction motor? And how can we understand the neat power requirement of from this test?
PLease anyone can tell me CTUM-15 specification?
how to calculate sizing of NGTR (Transformer rating,Loading resistor value and Current rating of resistor) and what is the X/R ratio. Details : 11kV,Capacitance 1.73532 micro farads,40kA for 1sec.
1 Answers Bhel, Indorama, Power Grid,
how to select the cable size? any formula to calculate cable size?
What is difference between Over Current & Earth Fault protection?
What is the purpose of Vector Group in transformer?
1 Answers Andritz, ThyssenKrupp,
difference between brush less & brush excitation in a generator?
my b-tech percentage is 50%. what answer will satisfy the hr ?
I BOUGHT A HAVELLS ACCL WITH GENERATOR STOP FASCILITY(i.e- BASICALLY IT IS A AUTO CHANGE OVER SWITCH) FOR MY HONDA EXK 2000S HOME GENERATOR (WHICH START IN PETROL & RUN IN KEROSENE). ACCL HAS 8 POINT. 2 FOR MAINS(PH & NUE), 2 FOR LOAD, 2 FOR GEN AND 2 FOR IGNITION POINT(X1 & X2). THE IGNITION POINT IS SPECIALLY FOR AUTO ENGINE STOP WHEN MAINS POWER RESTORE. I CONNECT THIS X1 & X2 POINT TO THE GENERATOR STATER MOTOR & EARTHING POINT. BUT WHEN MAINS FAILS THE GENERATOR COULD NOT START, BUT WHEN DISCONNECT THOSE X1 OR X2 POINT, THEN THE GENERATOR START. BUT WHEN MAINS ON THEN THE GENERATOR SHOULD START, AND WHEN I OFF THE MAINS THE GENERATOR AUTOMATICALLY STOP. PLESE HELP ME HOW I STOP THE GENERATOR AUTOMATICALLY WHEN THE MAINS RESTORE.