Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


How to calculate the electrical load for a standard telecom
BTS shelter and capacity of DG set required to cater to
this load?

Answers were Sorted based on User's Feedback



How to calculate the electrical load for a standard telecom BTS shelter and capacity of DG set req..

Answer / gkg

For Active load,voltage will be 48vdc or 24vdc,
so total active load=48v x 28A =1344w =1.34kw

passive load calc ok.

Is This Answer Correct ?    51 Yes 10 No

How to calculate the electrical load for a standard telecom BTS shelter and capacity of DG set req..

Answer / chandrashekar

Generally in telecom shelter only Passive and Activie load
will be available.
Passive loads are battery bank, PIU and Power plant. and In
active loads Concern BTS and Transmission load.

Thumb rule to calculate DG rating is KW=KVA*PF(0.8) or
Efficiency

i.e KVA=KW/PF


Example to calculate the rating of DG.

If total Load is available 15Kw both active and Passive
then

we should apply above formula KW=KVA*0.8

15=KVA*0.8 KVA = 15/0.8=18.75KVA
we can consider nearest rating of DG i.e=20KVA








Active Load Calculation:

Say a shelter is having only 1nos of BTS,Each BTS will
consume 20A to 30A load current depends up on type and make
of the BTS. average if we take 25A.
Transmission load for each BTS is about 3A total
transmission load current is 3A.
Now the Total Active Load current is =25+3=28A

Total Active load is P=VI P=230*28=6.4KW

Passive Load Calculation
1) AC Unit 2tr 1No the load is =7KW
2) All Internal Lighting and other =1KW
total passive load is 8KW now the toatl active and passive
load is =6.4+7+1= 14.4 KW round off 15KW.
for 15KW load 20KVA Dg set is sufficient

NOTE: always we should consider 1.5% extra rating because
starting current will always 1.5 % higher than load current.

Is This Answer Correct ?    56 Yes 25 No

How to calculate the electrical load for a standard telecom BTS shelter and capacity of DG set req..

Answer / dhananjay vats

VXI(BTS LOAD)=W/1000=KW.....A
8% LOAD LOSSES IN KW.........B
10% B.B CHARGING LOAD (EX-600AH, 60AX54V/1000)....C
INCOMING LOAD IN KW....C
AC IN KW (EX-1TR, 1TR-1350W, 1.3KW)......D
TOTAL ADD IN KW=A+B+C+D.....CONNECTION EB IN KW
KW=KVA/P.F

Is This Answer Correct ?    4 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

I hv a question regarding power factor improvement just after transformer. I request you to reply me plzz. thank you sir. My friend has a small unit of fabrication. in his factory the main load is a welding machine, lathe machine, grinding machine. this load is not continuous type. now our electricity board has installed 16 KVA, 11000/433 V transformer for our factory. In the energy meter (trivector meter) at LV side of transformer, i hv seen power factor value of 0.15 only when only 3 KW load was flowing. Further electricity board has suggested to install 4 KVAR capacitor at LV side after energy meter. Now my question is that if we permanantly install and switch on 4 KVAR capacitor after energy meter, during some load on transformer and also without any load on transformer, wht will be the power factor shown in energy meter?i dont want to get any penalty by electricity board, so plz suggest me if i can permanantly install and switch on the 4 kvar capacitor or not at LV side of transformer just after energy meter? Thank you again and awaiting for ur positive reply soon.

9 Answers  


Why neutral wire is heating in symmetric single phase distribution of three phase power supply?

2 Answers  


what is the need of capacitor in transmission lines?and how it works.

2 Answers   SCCL,


what is LT & HT?

6 Answers  


what is the basis for selection of Protection CT class ? How anyone can decide whether to go for 5P10 or 5P20 ?

3 Answers  


To determine the Healthiness of Insulation we will be performing Dielectric tests i.e Insulation Resistance test, Partial Discharge test,Switching Impulse, Lightning impulse, Tan Delta test ...etc why we required to perform this many test, why cant we do only one test. for Transformer, CT's

1 Answers  


What is the maximum allowed kwa through 2.5mm cable. Electric company installed 2 electric meter at my premises . Two jumper wires of 2.5 mm are used to connect . 2 single phase meters with allowable load 6 and 3 kwa. These jumper wires are taken from a 3 phase electric meter. Meters are in open Sun. What max load these wires can take.

0 Answers   KESC,


I have 1500KVA transformer ,How much Maximum KW Load is allowed?

15 Answers   GKC Projects Limited GKCPL,


Could the power factor on electrical system can affect the registration of the kwhr meter or the CT/PT? 

0 Answers  


Short circuit voltage of a transformer mainly depend on A ohmic resistance of primary B ohmic resistance of secondary C magnitude of leakage flux D cross sectional area of core

1 Answers  


why stay insulator is not used with stay wire for 11kv Lines. Whereas it is used for LT lines ?

2 Answers   Essar,


how can we calculate the ampacity of the electrical wire/cable. and what are the factors must be considered. pls. elaborate.

0 Answers   Webel,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)