How to calculate the NGR value for a 2.7MVA Transfomer,
11KV system where the fault current has to be limited to
50A?
The value of the NGR to be inserted in the cicuit can be
calculated by the simple formula
R = V / (√3 * I)
Where V is the System Line voltage in Volts
I is the value of the fault current to be limited in your
case it is 50A.
In general practice the fault current is limited to the
full load rating of the largest equipment available in the
system.
Is This Answer Correct ? | 6 Yes | 4 No |
what is the procedure for erection of a transformer
While connecting bulb in Series/Parallel,there is any difference in glowing
Between rotating armature type and rotating field type arrangements which one is adopted for large rated alternators and DC generators.Why there is difference in the choice?
What is the possible cause for failure of lightning arrestors in outdoor substation under normal condition
If a surge divertor is required to be protected by 32 amp C Curve Circuit breaker does this limit the amount of protection from surges that you will acheive
what is the need of representing AC power in sinusoidal waveform? why not in square or rectangular etc...
why we not connect the 12 V batteries in parallel to get the more backup supply for an UPS ? wheter off line or on line UPS ?
sir please tel me how calucalte kwh if home taken load 30ams how maney kwh taken per day.and 3phase motor 5hp per hars how maney load teken and how mach kwh and forward me to electrical table for calicalte kwh and kvr and kvah
if a.c supply is given to the motor,, what happen?
how many load we can take for lighting
Hai I have 2500KVA,Transformer,13.8KV/380.DELTA/STAR.How much load that I can take interms of current?How can I calculate also when I have loads in KW?
When one of three series resistors is removed from a circuit and the circuit is reconnected, the current