How to calculate the NGR value for a 2.7MVA Transfomer,
11KV system where the fault current has to be limited to
50A?



How to calculate the NGR value for a 2.7MVA Transfomer, 11KV system where the fault current has to..

Answer / pavan

The value of the NGR to be inserted in the cicuit can be
calculated by the simple formula

R = V / (√3 * I)

Where V is the System Line voltage in Volts
I is the value of the fault current to be limited in your
case it is 50A.

In general practice the fault current is limited to the
full load rating of the largest equipment available in the
system.

Is This Answer Correct ?    6 Yes 4 No

Post New Answer

More Electrical Engineering Interview Questions

what is the procedure for erection of a transformer

1 Answers   TCE,


While connecting bulb in Series/Parallel,there is any difference in glowing

3 Answers  


Between rotating armature type and rotating field type arrangements which one is adopted for large rated alternators and DC generators.Why there is difference in the choice?

1 Answers  


What is the possible cause for failure of lightning arrestors in outdoor substation under normal condition

0 Answers  


If a surge divertor is required to be protected by 32 amp C Curve Circuit breaker does this limit the amount of protection from surges that you will acheive

0 Answers  






what is the need of representing AC power in sinusoidal waveform? why not in square or rectangular etc...

8 Answers   Lanco,


why we not connect the 12 V batteries in parallel to get the more backup supply for an UPS ? wheter off line or on line UPS ?

2 Answers  


sir please tel me how calucalte kwh if home taken load 30ams how maney kwh taken per day.and 3phase motor 5hp per hars how maney load teken and how mach kwh and forward me to electrical table for calicalte kwh and kvr and kvah

1 Answers  


if a.c supply is given to the motor,, what happen?

0 Answers   Bhel, L&T, MSEB,


how many load we can take for lighting

0 Answers   ABB,


Hai I have 2500KVA,Transformer,13.8KV/380.DELTA/STAR.How much load that I can take interms of current?How can I calculate also when I have loads in KW?

10 Answers   L&T,


When one of three series resistors is removed from a circuit and the circuit is reconnected, the current

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)