How can we calculate ngr resistance for a generator and
Transformer ?
What type of transformer requires ngr ?
Answers were Sorted based on User's Feedback
Answer / ramesh
NGR-Neutral Grounding Resistor.It is used to limit the
fault current in the neutral line.calculation based on fault
current in stator in generator and star side in trfr
Is This Answer Correct ? | 25 Yes | 4 No |
Answer / ravi kumar purohit
DESIGN AND SELECTION CRITERIA OF
NGR
Neutral Grounding Resistor:
The power transformer secondary 6.6kV neutral shall be
medium resistance earthed in order to limit the 6.6kV
system earth faults to low values such as to limit
excessive damage to 6.6kV equipments.
Also that the earth faults are not too low value to cause
earth fault relay non-operation.
System voltage = 6.6kV
System voltage per phase = 6.6/√3
Vph = 3810.6Volts
Earth fault current (I) =50A for 5 sec
NGR calculation is done on the basis of following formula,
Vph= I X R
R= Vph / I
R= 3810.6/50
Resistance= 76.21 Ohms
NGR Selected is 6.6kV , 50A, 76.2Ohms, 5sec.
Normally 50 A
Is This Answer Correct ? | 21 Yes | 3 No |
The value of the NGR to be inserted in the cicuit can be
calculated by the simple formula
R = V / (√3 * I)
Where V is the System Line voltage in Volts
I is the value of the fault current to be limited
In general practice the fault current is limited to the
full load rating of the largest equipment available in the
system.
Is This Answer Correct ? | 6 Yes | 5 No |
Answer / madivalanagaraja@gmail.co
It is similar to the ground resistor calculation for transformer
The typical example was answered earlier for transformer dt.19-06-2009
Neutral of transformer can be grounded solidly earthed OR with Neutral Grounded with Resistance.
Typical shunt calculations fro 5 MAV 11/6.6 kv transformer neutral are as :_
Transformer rating = 5 MVA
Voltage ratio = 11/6.6 KV
Vector Group = Dyn11 (6.6 KV ground through Resistor)
During Earth fault voltage between Neutral
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / a s bhandari
Ohmic value of neutral grounding resister for a transformer is calculated as follows:
R = Vph/ I where I - value of fault current to be limited to flow through the neutral path, normally it is 50A for 5 sec.
Based on above, for 6.6 kv star side of a transformer
resister value shall be 76.21ohm.
Is This Answer Correct ? | 0 Yes | 3 No |
Is itnecessary to use capacitor in an Fluorescent Tube Light Fixtures? Why? What if not capacitors are not included?
When MICC cables used ?
how we calculate size of exciter(excit. volt and current) for generator?
when we megger is not damaged when we are measuring very low resistance? high d.c. voltage is produced in megger so according to i=V/R. current will be high so what is the reason ?
what is the load amp of a 2 hp single phase motor?
Do you know the overhauling of a motor?
Electrical 'C' license full abbreviation , and full form
2 hp motar how many amps taken please show me the formula
what is function of INVERTER
how to caculate cable size for diff types of loads? if anyone know the calculating procedure please tell me
why back up fuse used in vacuum magnetic contactor?
WHY STABILIZER SHOULD USED