How flow control valve is working with pnuematic positioner
and I/P convreter from command is given from remote
Answer / carl_ellis
A controller (the remote device) generates an electronic
4-20mA output signal which tells the valve what its position
should be.
The 4-20mA signal is an input to an I/P
(current-to-pneumatic) transducer, which creates a pneumatic
output signal proportional to the 4-20mA electronic signal
from the controller, probably a 3-15psi pneumatic signal.
The pneumatic control signal is an input to the pneumatic
positioner, which mechanically senses the valve's position.
The positioner drives the actuator with as much supply air
pressure as is necessary to drive the valve to position
demanded by the control signal.
Carl Ellis
Measure First
Is This Answer Correct ? | 2 Yes | 0 No |
why use 50% lel methane gas concentration for gas detector calibration instead of 60% lel gas concentration whereas the hi alarm set at 60% lel.
what's meanning of 1250KVA and how to calculate with Volttage and Current. answer give with example.
the basic of a DP flow transmitter are the following
selection criteria of control valve? and selection criteria of actuator explain in brief?
what is installation and commissioning of (fat & sat) of power plant dcs ? this question keeps in desirable conditions of one company .
what step is taken for ESD ( emergency shut down) in DCS REPLY to hashimka20009@gmail.com
0 Answers Bosch, Eskom, Sabic,
how ranges is decided for drum level or dearator level,in my pplant i have seen for boiler drum range is -1000 to 1000mmwc, while for dearator -2000 to 0 mmwc ,why they decided to take this range ?
what is the different between plc and dcs ? I know full name of this two but I want to know what structure and working style and speed I/O capacity and controller difference?
Explain ratio control system.
define SIMULATION a and what is the need of it
please send me hpcl placement papers
meaning of SMART