Answer / carl_ellis
A controller (the remote device) generates an electronic
4-20mA output signal which tells the valve what its position
should be.
The 4-20mA signal is an input to an I/P
(current-to-pneumatic) transducer, which creates a pneumatic
output signal proportional to the 4-20mA electronic signal
from the controller, probably a 3-15psi pneumatic signal.
The pneumatic control signal is an input to the pneumatic
positioner, which mechanically senses the valve's position.
The positioner drives the actuator with as much supply air
pressure as is necessary to drive the valve to position
demanded by the control signal.
Carl Ellis
Measure First
| Is This Answer Correct ? | 2 Yes | 0 No |
Can anybody tell me application of PLC,DCS,SCADA.
How we are blocking 40 kg or more pressure through only 6 kg instrument air in control valve
the pump holds on run indication into the dcs and filed local control panel remote push button condition operaton wrong like when the push button pushing conditions the pump is off and the push button release condition the pump is on totally opposite condition . And control room inside give the stop command into dcs just 1secon relay engage and again normal condition. How can I slove
I want to buy a seal kit of a pneumatic power cylinder.But I don't know it's specification.So please help me to know its specification.
How to find out turn down ratio of Pressure transmitter?
what is the difference between RS 232,RS 485,RS 422, how they different from each other
What are the reliability data ,like failure rate etc,for bently nevada systems & vibration probes.
if my 6 kva UPS gives 20 min. backup at 100 % load, then at 25% load what is the backup time?
What is Erosion in a control valve?
explain Cascade Control strategy with the help of a block diagram. also exlain its working in a distillation column
how can I install "operating system " in may HART communicator? It is damaged, and it doesn't boot up.
Why mixer nd grinder Is example of constant torque load not variable torque load ???
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)