how the testing of CT OF 400/200/100 done in33/11 kv s/s
actually the ct used in ss is in the range of 400-200-
100/1A.THE MAIN TESTS CONDUCTED ON CT'S ARE TWO 1.IR VALUES
FINDING TEST AND 2.RATIO TEST
1.IR VALUES ARE FINDING THROUGH 0.5,1,2.5,5KV STEPPED
MEGGER.GENERALLY IN APTRANSCO USES MOTARISED RIKEN MAKE
MEGGER.
2.RATIO TEST CAN BE CALCULATED BY PRIMARY CURRENT INJUCTION
KIT.
AND THE 3. GENERAL TEST IS POLARITY TEST.
| Is This Answer Correct ? | 8 Yes | 0 No |
what is the speed of current?
what is leading power?
what will be happened when a single phase motor is supplied by the dc supply
y we are used signal conditioner in capacitive transducer
why we somewhere use ryb phase sequance, somewhere use uvw, and somewhere abc??
for 5KW resistive load can anyone please suggest me whether to go for UPS/Inverter or Generator depending upon cost calulations
How many types of interlocking use in screw type air compressor,make-Kaser(BSD MODEL)?
0 Answers Automobile, Siddhi Vinayak,
Why generation voltage in thermal power plant is between 11kv to 33kv?
what is REF relay?
What are the effects of adding a zero to a system?
please explain to me how to calculate current,voltage,resistance with formula??
How to know motor winding is star or delta connected without see the information table and winding connection ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)