how the testing of CT OF 400/200/100 done in33/11 kv s/s



how the testing of CT OF 400/200/100 done in33/11 kv s/s..

Answer / vksumanth

actually the ct used in ss is in the range of 400-200-
100/1A.THE MAIN TESTS CONDUCTED ON CT'S ARE TWO 1.IR VALUES
FINDING TEST AND 2.RATIO TEST
1.IR VALUES ARE FINDING THROUGH 0.5,1,2.5,5KV STEPPED
MEGGER.GENERALLY IN APTRANSCO USES MOTARISED RIKEN MAKE
MEGGER.
2.RATIO TEST CAN BE CALCULATED BY PRIMARY CURRENT INJUCTION
KIT.
AND THE 3. GENERAL TEST IS POLARITY TEST.

Is This Answer Correct ?    8 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

Why Power factor is different - different in all three phase of a 3 phase nduction motor.

2 Answers  


What will be the fault current of any system when its generation is 10% of BASE generation( FUll Load )?Will is 10% or the same as full base calculation?

0 Answers  


why neutral wire don't shock?

9 Answers  


y we use neutral,all r told its used to for closed path..k its a just used to closed path,in a transmission line y we put same conductor used n both phase and neutral..if we use less than phase conductor in neutral mean we ll reduce cost its right r wrong..if we use mean any problem occur in transmission line..

0 Answers   ME,


Dear sir, I completed DECE In the year 1995.Now i am working in a private company from last 10 years as an Electrical supervisor.The company having a 1000 KVA transformer.Now i try to apply "C" Licence. I am eligible or not.If not eligible,pls give solution.

0 Answers   Balavigna,






why we use two slope(differential & restraining) in differential relay.but in busbar protection differential we are using only one slope?please explain

0 Answers   ISRO,


What is the maximum allowed kwa through 2.5mm cable. Electric company installed 2 electric meter at my premises . Two jumper wires of 2.5 mm are used to connect . 2 single phase meters with allowable load 6 and 3 kwa. These jumper wires are taken from a 3 phase electric meter. Meters are in open Sun. What max load these wires can take.

0 Answers   KESC,


How do ACB are maintenance, what are the problem occurred in ACB

1 Answers   KIML,


what is vch ?

1 Answers   CTS,


Why CTs are connected in star on T/F delta connected winding side & in delta on T/F star connected winding side for T/F differential protection?

2 Answers  


how many desk top computer can connect to a 25kva 3phase generator?

1 Answers  


What is on line ups and off line ups?

2 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)