how the testing of CT OF 400/200/100 done in33/11 kv s/s
actually the ct used in ss is in the range of 400-200-
100/1A.THE MAIN TESTS CONDUCTED ON CT'S ARE TWO 1.IR VALUES
FINDING TEST AND 2.RATIO TEST
1.IR VALUES ARE FINDING THROUGH 0.5,1,2.5,5KV STEPPED
MEGGER.GENERALLY IN APTRANSCO USES MOTARISED RIKEN MAKE
MEGGER.
2.RATIO TEST CAN BE CALCULATED BY PRIMARY CURRENT INJUCTION
KIT.
AND THE 3. GENERAL TEST IS POLARITY TEST.
Is This Answer Correct ? | 8 Yes | 0 No |
Why Power factor is different - different in all three phase of a 3 phase nduction motor.
What will be the fault current of any system when its generation is 10% of BASE generation( FUll Load )?Will is 10% or the same as full base calculation?
why neutral wire don't shock?
y we use neutral,all r told its used to for closed path..k its a just used to closed path,in a transmission line y we put same conductor used n both phase and neutral..if we use less than phase conductor in neutral mean we ll reduce cost its right r wrong..if we use mean any problem occur in transmission line..
Dear sir, I completed DECE In the year 1995.Now i am working in a private company from last 10 years as an Electrical supervisor.The company having a 1000 KVA transformer.Now i try to apply "C" Licence. I am eligible or not.If not eligible,pls give solution.
why we use two slope(differential & restraining) in differential relay.but in busbar protection differential we are using only one slope?please explain
What is the maximum allowed kwa through 2.5mm cable. Electric company installed 2 electric meter at my premises . Two jumper wires of 2.5 mm are used to connect . 2 single phase meters with allowable load 6 and 3 kwa. These jumper wires are taken from a 3 phase electric meter. Meters are in open Sun. What max load these wires can take.
How do ACB are maintenance, what are the problem occurred in ACB
what is vch ?
Why CTs are connected in star on T/F delta connected winding side & in delta on T/F star connected winding side for T/F differential protection?
how many desk top computer can connect to a 25kva 3phase generator?
What is on line ups and off line ups?