How to isolate a DPT from line in the condition that process
must not be disturbed,and process is also critical and no
bypass is available.?
Answer Posted / muhammad arsalan afzal
isolate the transmitter from the main isolation valve and
follow this procedure.
First of all
1= Close high pressure manifold valve
2= open the equilizing valve
3= than close the low pressure manifold valve.
Mostly we we open equilizer valve when we are isolating
the tx. but what will happen if we close high side pressure
valve before equilizing valve? applied process Pressure is
already there on both sides of the transmitters no extra
pressure will be exerted on the tx because we are only
closing the valve. DP cell demage only in that case if we
purge high or low side before closing the manifold
isolation valves and we start closing the valve without
opening the equilizer.
Is This Answer Correct ? | 0 Yes | 0 No |
Post New Answer View All Answers
Full form of KKS when use DCS.
what about your moleg in pogrees with company
what is droop in governer ,type of droop ,how it work
WHY THE DEGREE OF VALVE PLUG AND VALVE SEAT IS SLIGTLY DIFFERENT I CONTROL VALVE TRIM DESIGN
diff between neutral ,ground,phase , earthing and shielding?
what is the input of digital counter during the the calibration time?
What is the meaning of wet leg
Q1]IF THE RANGE FOR FLOW IS -35 TO 125 WHAT WILL BE THE SPAN FOR ABSOLUTE AND FOR NORMAL? Q2]HOW TO CALIBRATE CAPILLARY TYPE LT? Q3]HOW MANY ERROR CALCULATIONS ARE THERE USED IN PROCESS INDUSTRIES? Q4]HOW TO CALIBRATE TEMPERATURE TRANSMITTER? Q5] HOW TO CALIBRATE LEVEL TROLL AND HOW TO CONNECT? Q6]PLEASE TELL ME THE BASIC FOR INSTRUMENTATION WHICH IS APPLIED FOR CALIBRATION AND FOR ALL? PLEASE MAIL THE ANSWER TO honest_yes@yahoo.in
Which topics are covered in Process Control?
why we use 3 wire rtd direct wiring for temperature measurement instead of temperature transmitter like bearing temperature
List three types Level Gauges with their working principles
Operational amplifiers
what is the vital subject for scoring bhel exam&what is the question pattern
when the instrument tapping on pipe line is located below and transmitter is located above the tapping point for liquid service transmitter, what should we do, is there any additional drain valve is required??
why we take %i0.0 as input for twido plc