present we are having 0.8pf but I want increase it up to
0.99 so what is the formula for it and how can i calculate?
Answers were Sorted based on User's Feedback
Answer / kuppuswamy
PF = KW/KVA That is power factor = True power divided by
Apparent power.
If you want to increase the PF in generator, you have to
adjust the speed and voltage to bring to the required PF.
If you want to increase PF in industrial load, you have to
go for adding the capacitor banks in the line side.
Is This Answer Correct ? | 7 Yes | 0 No |
Answer / satheeshramesh
If u wish to increase the P.F from 0.8 to 0.99 u have to
add capacitor banks.
Capacitor rating required (kVAR) =kW(tanØ1-tanØ2)
Cos Ø1 = 0.8, Ø1 = cos-1 (0.8), tan Ø1 = .
Cos Ø2 = 0.99, Ø2 = cos-1 (0.99),tan Ø2 = .
Is This Answer Correct ? | 7 Yes | 0 No |
Answer / at
if you want to increase the power factor from 0.8 to 0.99
then in that case for
1. Generators:- you will have to increase the excitation
when generator is connected in an interconnected system
i.e. Many generators operating in parallel / or connected
to grid. increasing the excitation gives a leading power
factor and under excited generated draws lagging power
factor power.
2. When it is the case of Industries or other utilities
consuming electrical energy. one should know that all loads
consuming power are 99.99% inductive loads.Thus by adding a
capacitor bank of suitable rating shall be required to
compensate the lagging power factor.
Is This Answer Correct ? | 1 Yes | 0 No |
Control cables in S's will carry 1000v which is AC R DC? Pls answer me
What is working Priniciple of TVSS ????
what is power factor
what is auxilliary transformer??
what is mean by harmonics?Type of harmonics?
What is the difference between INVERTER and UPS?
how to interlock 2 incomer,1 buscoupler MCCB,like we interlock an ACB... pls answer this question and if possible send me the ckt diagram..
2.5mva transformer is installed in our company with oltc but it is not working in auto mode ,it is operative in manual mode control wiring is done how can i rectify it?
MY QUATION IS ABT THE MAIN POWER TRANSFORMER IN STEEL PLANT , I WISH TO KNOW THAT WHY TRANSFORMER PROTECTION NOT TRIP AS CABLES ON THE SECONDAY SIDE IS WATER COOLED. TRANFORMER DETAIL NORMAL KVA--150 KVA PRIMARY VOLTAGE --34.5 KV SEC.NO-LOAD VOLTAGE---1.290-908-690V ( WITH PRIMARY DELTA CONNECTED) CONNECTION--D/d (EXTERNAL CLOSED) CONSTANT RATEING FROM--1.290-908V CONSTANT CURRENT FROM--908-690 VECTOR GROUP--D III
what is a bus post insulator? explain its application in a substation.
Please give me a solid reason there are 2 ELCB's If we take Phase from ELCB NO:1 an Netural from ELCB N:2 why ELCB is tripping when we connect the Load?please brief me with detail
What are the advantages of stationary armature and rotating field system?