What are the possible causes of REF operation on a power
transformer
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
All cts(Phases and neutral) are connected in parallel.If
there are unbalanced currents in phases, the resultant
current in REFR is zero as the difference is also measured
by NCT .If there is an earth fault inside the transformer
or between cts and bushings ,the fault current is sensed by
NCT only. Hence current balnce is lost in REFR resulting in
trip command by the relay
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / k.prakashchandra
Please note that REFR will not act under earth faults in
phases beyond the CTs. As its coverage is limited
(restricted) to Tr only ,it is called ristricted earth
fault relay.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / k.prakashchandra
An earth fault between CTs of primary and secondary sides,
as the fault current will not pass through secondary side CT
| Is This Answer Correct ? | 2 Yes | 2 No |
actually i dont know the answer but i wanted to know what
is the REF operation of power x'mer...plz explain in detail
| Is This Answer Correct ? | 1 Yes | 1 No |
what is the principle of the single phase energy meter? and,what is the advantages and disadvantages of single phase energy meter?
what is resistance
Air circuit breaker safety
Why are the cores of large transformers built up of circular transactions ?
I want to know what must the CT ratio be on a load of 300A is a 3PH nutral to earh installation?
What is the actual meaning between the energy conservation and energy saving ?
How to calculate the External Resistance required for 60HP slipring motor in case no any data of the Motor is available???
for which possible reasons a motor can fail to start??
Why in KVA diesel engine? Why not KW
i am using auto transformer for starting of induction motor to provide reduse voltages...but the principle of a tansformer according to definition"which transform energy to on circuit to another circuit with constant power and constant frequency". so if i am using reduse voltage then current obsely hige because power is same.but we use auto transfarmer for starting of induction motor to give low current.but here according to definition we are giving hige current.
how we select the fuse and OLR rating for 3 phase induction motor from 1HP TO 100 HP?
Why reverse relay used
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)