What are the possible causes of REF operation on a power
transformer
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
All cts(Phases and neutral) are connected in parallel.If
there are unbalanced currents in phases, the resultant
current in REFR is zero as the difference is also measured
by NCT .If there is an earth fault inside the transformer
or between cts and bushings ,the fault current is sensed by
NCT only. Hence current balnce is lost in REFR resulting in
trip command by the relay
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / k.prakashchandra
Please note that REFR will not act under earth faults in
phases beyond the CTs. As its coverage is limited
(restricted) to Tr only ,it is called ristricted earth
fault relay.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / k.prakashchandra
An earth fault between CTs of primary and secondary sides,
as the fault current will not pass through secondary side CT
Is This Answer Correct ? | 2 Yes | 2 No |
actually i dont know the answer but i wanted to know what
is the REF operation of power x'mer...plz explain in detail
Is This Answer Correct ? | 1 Yes | 1 No |
when a cunductor is being disconnected from live cct, still it showing charged, if its checked by line tester?
What is the basis for selecting Vk/2 or Vk/4 for REF and Differential protection of Transformer and What is the significance of magnetising current
If you don’t have coal, salt and copper, then how would you earth your connection temporarily at a camp site.?
What size cable is used for HT cable to the transformer of 630kVA, and the supply voltage is 11kV
How many percent of power are not being registered if we bypass one side of the meter base terminal using #8 cu wire on 1-phase kwhr meter.
what is the meaning for va and how it is generated
What is the slip speed?
Why we use Electrical energy rather than any other type of energy, mostly? Explain behavior of open secondary CT and short circuited secondary PT in energized condition?
if a single phase 3 hp submersible pump of Crompton Greaves is moving in reverse direction and sometimes it moves in rigth direction ,then what may be the cause....
In a flange coupling, the flange bolts are designed for
why transmission voltage is 230kv and not 220kv which is a multiple of 11
1 Answers Mettur Thermal Power Station, Siemens,
what happen ,if generator will generate leading power factor?