What should be the DC voltage for Hi-pot test on 11kv switchgear
Answers were Sorted based on User's Feedback
Answer / gunasekaran
calculation is (2E+1)1.414
(11*2+1)1.414=23*1.414=32.52*.85=28kV already HV test done
at factory so we have applie only 85%of rated voltage
| Is This Answer Correct ? | 12 Yes | 5 No |
Answer / solanki
i think it will be the around 23 kv for the 11 kv switchgear
bcz its take the calculation twice of rated switchgear voltage
| Is This Answer Correct ? | 4 Yes | 9 No |
how to stop oil leakage in power transformer.
What the full form of KVARs
What is the acceptance value of leakage current in HI POT test
magnetic circuit consume energy
How to Calculate IKW(input kilowatt)of a Chiller plant
what are feeder pillars & panels?
WHAT WILL HAPPEN IF WE START A MOTOR WITH STAR & IT IS RUNNING WITH STAR CONNECTION INSTEAD OF DELTA
what is back emf?
What is the disadvantage in proportional controller?
any earth foult trip the relay but in welding time not trip by earth foult
0 Answers Power Grid, Siemens,
Why sometime AVR and sometime Booster coil is used in Alternator? what is the diferance between AVR & Booster coil due to which they are selected
why SCR use in power plant
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)