Answer / c.hari balakrishnan

SWITCHGEAR : -

There is no specified value of leakage current,Normally it
depends on how much load is connected.Normally it is in
milliamps.For example : In 11kV SWGR we highpot with 20bays
(indoor SWGR)we can get around 20 to 30 mAmps...

Cable: -

for cables normally we can get around very low Milliamps...

Is This Answer Correct ?    8 Yes 8 No

What is the acceptance value of leakage current in HI POT test..

Answer / tharindu eroshan henadawithara

3 mA for 11 kv for my sites,and really it is possible in 3c240 xlpe/pilc joints(new ,short distance).
3c240 pilc possible with 8mA max(length and old)
dry country with under ground system.
no rain at all..(no effects from water,but may from see)

Is This Answer Correct ?    1 Yes 3 No

Post New Answer

More Electrical Engineering Interview Questions

who & how the notations given as RYB to 3phase power supply.

1 Answers  


why the rating of dc generator is in kw where as rating of alternator is in kva?

3 Answers  


what is the highest transmission voltage in India till now?

36 Answers   Bhel, Electrical,


what happened when we supply a dc current in dc motor?? can it worked properly?

0 Answers  


How equivalent impedance is calculated in thevenin theorem?

0 Answers  






how is positive, negative, zero sequence is happen.. how is effect on 3 phase system

0 Answers  


what do u mean by PS-0.2-5P class of Ct

3 Answers   ABB,


Can you explain the phase displacement between primary and secondary of power transformer of any vector group(for ex)?

1 Answers  


What if high voltage side circuit breaker of a ehv transformer instead of lvcb? Kindly elaborate.

0 Answers   MSETCL Maharashtra State Electricity Transmission Co Ltd,


How can eliminate noise problem inside temperature controller temp. variation due to contactor chattering problem.

0 Answers  


CT Ratio of a energy meter connection is Red Phase : 100/5A, yello Phase : 50/5A & Blue phase : 100/5 A what is the overall Multiplication factor

0 Answers  


1.what is the difference between transformer differential and busbar differential.2)why we are using 2 slope for trafo diif and 1 slope for busbar diff.3)what is the purpose of metrosil and stabilizing resistor in high impedance relay circuit.4)how metrosil reduce the peak volage.5)what is the funtion of stabilizing resistor

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)