how to estimate the breaker capacity of breaker,please give
the one example( 6.6 kv breaker,800a)?????
Answers were Sorted based on User's Feedback
Answer / praveen
breaker capaciy taken by 132kv for example 133*1.55 times
capacity 145kv suitable for beaker
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / raghavendran.r
Step1: Calculate the system MVA.I have calculated that as 1.732*6600*800 = 9.144MVA. I have taken it as 10 MVA for easy calculations further.From the system MVA find out the Fault MVA value using the per unit impedance.i.e
Fault MVA = System MVA /P.u.Impedance.I am taking iot as .1
Hence we arrive at the Fault MVA.From this condition we get to know the Short circuit current as Isc = Fault MVA/Sys Voltage(6.6kV).
Usually, for a 6.6 kV system, the short circuit withstand rating is 40kA for 1 second.The Momentary current or making current is 2.55 times the Max. short circuit current.hHence we arrive at 100kA(Peak)
Is This Answer Correct ? | 2 Yes | 2 No |
What is the permissible value of earth resistance!
What is the deffrence between Siemens S7-300 & S7-400 PLC?
how to find the voltage's of a transmission line plzz help with pictures i am not able to understand
why are we using resistor in NGR ?
I try to check the three phase voltage in multimeter, in 125A isolator switch incommer. first i touch R phase, and then i touch Y phase using multimeter, the moment i touched, it blasts and that moment i got blindness. multimeter selector position is correct(750V AC MODE AND RED PROBE WASS IN v AND BLACK PROBE WASS IN COM. MODE. COULD ANYBODY GIVE ANSWER FOR THIS TO AVOID FURTHER ACCIDENTS PLEASE?
what is the principle of vvvf drive motor
Briefing the effects of ASR and ACR of a double closed-loop speed regulating system.
In synchronous generators field is rotor and armature is stator.Can we take the output at the rotor in case of synchronous generator by the dc excitation on the stator?
Resistance of a conductor in a close electrical ckt is practically zero why?
How to calculate the Short Circuit Impedance in Transformer?
when we conduct high voltage testing why milli amp. is required?
Please explain how to do 'tan-delta test' on AC generator? and where i get clear and brief detail, give any web page address.