Why we use 4 - 20 ma?
Answers were Sorted based on User's Feedback
Answer / sam daniel, marthandam, kanyak
To operate a Digital signal we need 1-5Vdc. For Analog
Instruments we are using 250 ohms as load resistance. When
we converting this signal into current By Ohm's
Law V=IR
I=V/R
Put, V=1V Then I=1/250=4mA
Put, V=2V Then I=2/250=8mA
Put, V=3V Then I=3/250=12mA
Put, V=4V Then I=4/250=16mA
Put, V=5V Then I=5/250=20mA
*Also, since this is linear region
*Not possible to cause spark
*Since it is a current signal we can transmit it into long
distance.
*Suppose if the instrument is dead we can identify it.
Is This Answer Correct ? | 62 Yes | 3 No |
Answer / jayaraj
1}///in earlier days we had used BJT transister in signal
conditioning circuits for amplification purposes so in BJT
transfer characteristics 4 to 20 milli amps is a linear
region,....but now-a-days we re using cmos only.... as a
convention only we are following this 4-20 range
2}///another reason...for not using 0 milli amp
coz if we use like that we cannot distinguish between true
signal zero and dead zero(break in wires)
Is This Answer Correct ? | 46 Yes | 2 No |
Answer / nileshkumar
1) 4 - 2 ma signal can transmited long distance without
signal drop in cable.
2) To operate a Digital signal we need 1-5Vdc. For Analog
Instruments we are using 250 ohms as load resistance. When
we converting this signal into current By Ohm's
Law V=IR
I=V/R
Put, V=1V Then I=1/250=4mA
Put, V=2V Then I=2/250=8mA
Put, V=3V Then I=3/250=12mA
Put, V=4V Then I=4/250=16mA
Put, V=5V Then I=5/250=20mA
*when two connection short no sparking.
*Since it is a current signal we can transmit it into long
distance.
*Suppose if the instrument is dead we can identify it.
Is This Answer Correct ? | 5 Yes | 1 No |
in 4-20ma we can easily check the zero and wire breaking in
transmitter. Analog card accept 1-5v dc supply. thatsy V-IR
I=V/R
V=1V R=250OHMS
1/250 = 4MA
V=2V THEN I=2/250 = 8MA
V=3V THEN I=3/250 =12MA
V=4V THEN I= 4/250 =16MA
V=5V THEN I=5/250 = 20MA.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / anish kumaran r
Live zero and minimum current required to keep alive the tx
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / suresh nagdeo
another reason from starting current from 4 ma is between two cables maximum induced current is always below 4 ma. if electrical and instrumentation cables running together this type problems arised.
Is This Answer Correct ? | 0 Yes | 0 No |
What is the different between of rtd and thermocouple ?
How to ensure vibration sensor functioning accordingly.With out using an other sensor.
how do i calibrate mmwc pressure guage with out calibrator.if any? pls give me the ans.
I saw one P&ID 6" control valve has been connected with 8" process line, and 2" valve also connected in parallel with 6" valve. why the 2" valve connected in parallel, Is there any technical reason. please clarify. With Regards-Kittu
Why we are using reverse action in displacer types level transmitters on some Vessels?
what is three element loop
What is the basic difference between 2 Wire, 3 Wire and 4 Wire RTD
Why flow/pressure transmitter before control valve?
calibration of instruments.
why are use only 4 to 20ma. signal.
how to calibrate a capillary type level transmitter for a closed tank in field? also what is the procedure for commissioning a capillary level transmitter for a closed tank?
What is the difference between local indicator(flow) and flow indicator?