how the 4 to 20 mA signal goes to any
controller/indicator,and what is the role of voltage ,12/24
and how to do connection of it, in controller.
Answer / carl_ellis
For a 2 wire loop powered transmitter, a DC power supply
supplies power to the transmitter to power its electronics.
The transmitter uses about 3.5mA of the loop current to run
its electronics.
The transmitter's electronics measures a physical property
(temperature/pressure) which creates a measurement value
associated with engineering units. The transmitter
regulates the loop current between 4.0 and 20.0 mA (by
varying its internal resistance to drop whatever voltage is
needed to create the correct current) so the current
represents a measurement proportional to the scale
configured for that physical property.
The controller/indicator is the primary 'load' with an
analog input that has a dropping resistor. The dropping
resistor creates an IR (voltage) drop the
controller/indicator uses for its A/D conversion.
A 2 wire loop powered transmitter has a lift-off voltage,
the minimum voltage needed to operate the transmitter with a
zero ohm load. As the loop load voltage increases, the
minimum voltage required to power the transmitter and the
loop load increases.
24Vdc is the typical, nominal power supply voltage used in
the process industries. Many 2 wire loop powered
transmitters will function with supply voltages up to about
40Vdc. Higher supply voltages are needed with long copper
wire runs where the wire resistance becomes a significant
load factor.
Carl Ellis
Measure First
| Is This Answer Correct ? | 0 Yes | 0 No |
Explain types of valves?
What are the maximum packet size of: a) HART b) Profibus DP c)Profibus PA d) DeviceNet e) Foundation Fieldbus
DC motor and DC Drives working funda?
what is the function of a diaphragm?
i want know about capillary type LT transmitter installation. we can install any location in between to HP and LP leg?
i install a DP transmitter of Faugi on drum level of boiler but i face a problem in it when i engergize the transmitter the meter shows 0 or 100% no variation in it.the distance of two points is 19.5 inches, i am in trouble please suggest me what can i do it's very urgent Please reply me as soon as possible Best regards ikraam haider
why we use the 4-20 mamp signal used for transmitter.
Draw a complete P&ID of a flow suction tank indicating all control & protection equipment. Indicate all its inlets and outlets. Explain the controls for this system
If Solenoidal valve works in manual mode but not in Auto mode. What should be the problem?
8 Answers Bharathi Cement, Titanium,
how to trim the pressure transmitter ?
What is pre-commissioning and commissioning ?
why pressure 3-15psi is used as industrial standard and what is the reason
2 Answers JAL International, UltraTech,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)