in 132 kv substation ligtning arrestor(120 kv) connected to
line. but line voltage comes to 132 kv, it operate or
not???
Answers were Sorted based on User's Feedback
Answer / vettum perumal
Ligtning Arrestors are connected across one phase and
earth. Hence,the insulation of the arrestor shall be
suitable for only phase voltage. that is, 132kv/root3 =
76KV.Hence, these 120 KV LA will operate very well.
Is This Answer Correct ? | 26 Yes | 0 No |
Answer / s.rajasekar
the lightinig arrestor connected with line in parrallel
then the volage range will divided by root 3.so the
insulation level of the arrester is suitadable for 132kv
system
Is This Answer Correct ? | 15 Yes | 3 No |
Answer / avradeep das
In any conductor of 132 KV transmission line rated voltage
with respect to ground(remember LA is connected between one
conductor/phase and earth)is 76(approx) KV so 120 KV is
adequate
Is This Answer Correct ? | 6 Yes | 1 No |
why transformer not work in dc
in 31.5 mva power transformer how to set of wti and oti?
When one of three series resistors is removed from a circuit and the circuit is reconnected, the current
Why electrons flow only one direction in semiconductors. why can not flow both directions
what is the voltage of insulation megger that should be used for measuring the resitance of 66kv equipments.
State nyquist stability criterion.
why some transformer without breather.
What is the approximate percentage of Si content in transformer core(CRGO-Cold Rolled Grain Oriented)? Why it is kept so low?
What is AVR in Generators and How is it working.
what is the minimum clearance between a 11KV 150KVAR capacitor cell and series reactor.can a series reactor can be mounted in the same structure of the capacitor cells structure
hello everybody. what does an abnormal stator winding impedance or dc resistance show? thanx
What are the main Electrical IS rules?