in 132 kv substation ligtning arrestor(120 kv) connected to
line. but line voltage comes to 132 kv, it operate or
not???
Answers were Sorted based on User's Feedback
Answer / vettum perumal
Ligtning Arrestors are connected across one phase and
earth. Hence,the insulation of the arrestor shall be
suitable for only phase voltage. that is, 132kv/root3 =
76KV.Hence, these 120 KV LA will operate very well.
| Is This Answer Correct ? | 26 Yes | 0 No |
Answer / s.rajasekar
the lightinig arrestor connected with line in parrallel
then the volage range will divided by root 3.so the
insulation level of the arrester is suitadable for 132kv
system
| Is This Answer Correct ? | 15 Yes | 3 No |
Answer / avradeep das
In any conductor of 132 KV transmission line rated voltage
with respect to ground(remember LA is connected between one
conductor/phase and earth)is 76(approx) KV so 120 KV is
adequate
| Is This Answer Correct ? | 6 Yes | 1 No |
how winding temperature detects in power transformer...?
at what basis/standard we have to arrive the current density of aluminium/ copper in busbar?
What is electrical diversity factor in electrical installations?
In pakistan appliances work on 220v at 50hz and in us appliances work on 110v at 60hz what is basic theory to explain it
Sparking occur when a load is switched off because the circuit has high – a.) Inductance b.) Capacitance c.) Resistance d.) None
define electrical field?
Why we are use dol starter up to 10 hp
We are getting supply at33kvand it stepdown to 11kv.So Our requirement is 11kv voltage.why we draw 33kv from the grid instead of 11kv?
What is Nominal voltage?
In our plant we have installed new MCC with ELR and CBCT which is detecting some leakage current in the system but it leading to some confusion when to check that in which feeder which is drawing current we put off the whole panel itself but still CBCT detecting some leakage current so can anybody ans me , where i am going wrong or how to detect whether its actual leakage or CBCT malfunctioning.
The series field winding has low resistance while the shunt field winding has high resistance. Why?
What type of surgery impedence with 200ohs
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)