How to calculate the breaking capacity(like 15ka,20ka) of Circuit breaker (MCB,MCCB,ACB)..

Answer / shan80

it depend upon the value of current flows during short
circuit.
And the short circuit current depends upon the KVA rating of
transformer how supplies that particular load and transformer
percentage impedance.

Is This Answer Correct ?    56 Yes 15 No

How to calculate the breaking capacity(like 15ka,20ka) of Circuit breaker (MCB,MCCB,ACB)..

Answer / jitesh patel

we must know load of perticular equipment.
For Ex. Our load in MVA is 50 MVA
Our system voltage(MCB,MCCB,ACB) is 440V.

I(Bre)= 50/(1.73x0.440)=65.6 =Approx 65KA.

Our load in MVA is 20 MVA
Our system voltage(MCB,MCCB,ACB) is 440V.

I(Bre)= 20/(1.73x0.440)=26.2 =Approx 25KA.

Is This Answer Correct ?    79 Yes 50 No

How to calculate the breaking capacity(like 15ka,20ka) of Circuit breaker (MCB,MCCB,ACB)..

Answer / ali

100A MCCB Bteaking capacity calculation

Is This Answer Correct ?    16 Yes 4 No

How to calculate the breaking capacity(like 15ka,20ka) of Circuit breaker (MCB,MCCB,ACB)..

Answer / mohammed rafi

All above said suggestions are mere copy paste of something from wiki answer.its totally wrong.
Aforesaid calculations are to calculate rated current.
Short circuit analysis is to be done to calculate breaking capacity.

Is This Answer Correct ?    11 Yes 3 No

How to calculate the breaking capacity(like 15ka,20ka) of Circuit breaker (MCB,MCCB,ACB)..

Answer / ashok

it depends on the short circuit & full load of equipment

Is This Answer Correct ?    24 Yes 20 No

How to calculate the breaking capacity(like 15ka,20ka) of Circuit breaker (MCB,MCCB,ACB)..

Answer / ranadhir roy

We need to find out the short circuit MVA & based on this shortcircuit MVA , we need to calculate shortcircuit current .

Is This Answer Correct ?    2 Yes 0 No

How to calculate the breaking capacity(like 15ka,20ka) of Circuit breaker (MCB,MCCB,ACB)..

Answer / sunil sethi

All are ok, but In industries generally 5MVA transformer they are using for a company load, then if we consider 5MVA is our load then Icu is 5/(1.732x440)=0.0065ka , please clarify, Is it ok please answer .

Is This Answer Correct ?    2 Yes 3 No

How to calculate the breaking capacity(like 15ka,20ka) of Circuit breaker (MCB,MCCB,ACB)..

Answer / t s gupta

Breaking Capacity of MCCB is pre-calculated permissible amount of fault current (value of current can flow from contacts before opening/tripping the MCCB without damaging) which may facilitate the safe operation of MCCB and distribution transformer both.
It shall be calculated/derived from the distribution Transformer MVA rating and %impedance = kVA*100/ system voltage of load side * % Impedance rating
e.g. 20 kVA transformer with 5% Impedance, secondary voltage 440V i.e. 0.440 kV
Fault current Isc = 20*100/.440*5 = 10kA approx.

Is This Answer Correct ?    0 Yes 1 No

How to calculate the breaking capacity(like 15ka,20ka) of Circuit breaker (MCB,MCCB,ACB)..

Answer / hrusikesh dehury

we must know load of perticular equipment.
For Ex. Our load in MVA is 50 MVA
Our system voltage(MCB,MCCB,ACB) is 440V.

I(Bre)= 50/(1.73x0.440)=65.6 =Approx 65KA.

Our load in MVA is 20 MVA
Our system voltage(MCB,MCCB,ACB) is 440V.

I(Bre)= 20/(1.73x0.440)=26.2 =Approx 25KA.

Is This Answer Correct ?    14 Yes 24 No

Post New Answer

More Electrical Engineering Interview Questions

For 7.5kw star delta starter how to calculate 1. Mccb rating 2. Contactor rating 3. Over load relay rating

1 Answers   L&T, MAHINDRA,


what is the difference between ac and dc generator

14 Answers  


What is dynamo function in DG sets and draw block diagram?

0 Answers   KPR Agrochem,


what is the Connected Load (kW) or Contract Demand (kVA)of mahindra nasik plant??

0 Answers  


How one may guess the direction from which the distribution line is incoming if there is no pole plate on poles?

0 Answers  






what is the effect if we add capacitor on DG supply, it has any loss or benefit.

6 Answers  


IF i have switchgear with busbar current rating of 1000Amp 35kA then is it necessary to have outgoing breaker kA rating to be equal to busbar kA rating?

6 Answers   L&T,


What is difference is of VSD,VFD,VSDS, are they the same as the direct current to control dc using above mention

0 Answers  


we have one pumping station and 4.6 MW 7 no.s synchronous motors.so there is no required HT capacitor to improve power factor.But we have two no.s of 25 Mva power transformer connect to distribute the power for motors connect with 220 kv line.So i have required the HT capacitor to improve power factor at HT side i mean power transformer bus side.So please suggest how much HT capacitor banks required for same.

1 Answers  


1.What is the proper definition of power system stability? 2.some times a blue spark is visible in the secondary side of a distribution transformer at the contact position of bushings and fuse wire,why?

1 Answers  


what are types of ups?

1 Answers  


how can we can take BDV test in transformer?

5 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)