How to calculate the breaking capacity(like 15ka,20ka) of
Circuit breaker (MCB,MCCB,ACB)
Answer Posted / shan80
it depend upon the value of current flows during short
circuit.
And the short circuit current depends upon the KVA rating of
transformer how supplies that particular load and transformer
percentage impedance.
| Is This Answer Correct ? | 56 Yes | 15 No |
Post New Answer View All Answers
What is the minimum value of hfe for the oscillations in transistorized rc phase shift oscillator?
How to select circuit breakers rating eg. if i select a circuit breakers of capacity 40 amps DC with operating voltage 28 volts and if i what to use same circuit breakers for 300 Volts DC application what is the current rating of this circuit breakers.
how to convert lv line to hv line and viseversa, any losses will occur during this process
Explain Creepage Distance of Insulator
howmany electrician should maintain for a 1000 kva used plant... in kerala..
If 24 KVA AVR having Input voltage 200-400v, Output voltage 415+-1%, what will be the voltage if Load is 13A.
Define the term factor of inertia.
Why field rheostat is kept in minimum position?
What are the uses of stepper motor?
I am B.E.electrical engineer having 7 years of experience in Transformer testing upto 315 MVA.I want to khow how I can get the 'Electrical Valuer' License.
Can anyone please provide me details of MCCB/Contactor/SFU rating calculations for a motor feeder..for example 50 kw.. not from type-2 cordination chart. i want manual calculations..
How much of the total hydro power potential has been exploited so far in india?
What are the two segments of nyquist contour.
what is residuel magnetism. and how order lead acid batteries for 24 volt. emergency lighting system.
Fantio of tranformer