Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


i have one transformer 1000kva, 11/.433kv. we are using
200/5 amp. ct unit for measuring purpose, & one 800 amp.
V.C.B Unit for the same t/f operate, i wants to known the primary
current of T/F is only 53 amp. why we used 800 amp.
V.C.B ? & 200/5 amp. CT Unit.

Answers were Sorted based on User's Feedback



i have one transformer 1000kva, 11/.433kv. we are using 200/5 amp. ct unit for measuring purpose, ..

Answer / vinit patil

You are right, you should fight with your electricity board
regarding the HT Metering CT ratio. You should actually
required 100/5 ratio.
But while deasigning VCB it is always prfarable to go on
higher side because it can sustain the heavy short circuit
current. One thing should be noticed that the protection
CTs should be as per the Primary current of the ransformer.

Is This Answer Correct ?    5 Yes 2 No

i have one transformer 1000kva, 11/.433kv. we are using 200/5 amp. ct unit for measuring purpose, ..

Answer / a k kataria

Well given the rating of transformer as 1000 kva, CT ratio
should have been 100/5. As far as VCB current rating is
concernd,these are generally made for universal
applications and are generally 630 Amps onwards 'cause in
the eventuility of fault ,heavy currents are to be taken
care of.More over increase in the rated current capacity of
breaker adds little to the cost compared to other
components of the breaker.There fore capacity of VCB is OK.

Is This Answer Correct ?    2 Yes 1 No

i have one transformer 1000kva, 11/.433kv. we are using 200/5 amp. ct unit for measuring purpose, ..

Answer / krishna chaitanya

first u must know that transformer transforms with
no change in power. As its 11 kv on primary side as
per funda you can calculate primary current 53 amps.
P = vi cos fi. A 100/5 ratio ct is enough to measure.
But its always advisable to select equipments with
larger than required ratings. Sometimes u'l see a
300/5 ratio ct.
and vcb, 800 amp vcb is for load. There'l be another
breaker at secondary of transformer with larger than
this amp rating. 800 vcb is provided for a particular
load control.
checkchaitu@yahoo.com

Is This Answer Correct ?    1 Yes 2 No

i have one transformer 1000kva, 11/.433kv. we are using 200/5 amp. ct unit for measuring purpose, ..

Answer / b2

Transformar steap down the voltage so current grow up high
so we are use 200/5 amp. ct & 800 amp.V.C.B

Is This Answer Correct ?    1 Yes 8 No

Post New Answer

More Electrical Engineering Interview Questions

A power transformer 4MVA/11KV/0.415Kv has been out of use in 12years. what maintenance actions/test need to be carried out before energizing.

0 Answers  


How does a VOLTAGE OPERATED DIFFERENTIAL RELAY work??

2 Answers  


1. What are the tests to be carried out for CBCT? 2. can measure the secondary resistances? 3. with respect to secondary maximum how much voltage can be applied for IR test.

0 Answers  


What is the difference between AMF panel and DG Synchronization panel? please define the working of both the panels?

3 Answers   ABB, Power Grid,


What is the difference between resistance grounding system and resistance earthing system?

0 Answers  


how many types are their in switchyard or substation(like D,I TYPE), what is differant between them

0 Answers  


dear all, in motor operation , motor is of 100 hp and bimetal relay setting is 130 amp, if relay is getting tripped on 120 amp balance current what can be the reason? Relay is newly replaced. I dont know but is there any frequency effect in thit case? Can frequency variation affect bimetal relay operation?

1 Answers  


In LT cables 3.5 core cable are available that means 3 core and .5 for neutral Why .5 for neutral and is there any reason for that please suggest thanks and regards pavan kumar

1 Answers   Sodexo,


how to reduce earth resistance in sandy soil.

1 Answers  


for a 500 KVA connected load, I calculated 30% of capactor for power correction. Even after using 225 KVR capactor PF is not improving. What could be reason for low Phase correction factor?

0 Answers   Power World,


If o/p power is doubled by how much does the sound increase

0 Answers   Flipkart,


what is Over current, earth fault (O/C+E/F) ?

2 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)