Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


how can we calibrate the differential pressure transmitter
by using HART communicator

Answers were Sorted based on User's Feedback



how can we calibrate the differential pressure transmitter by using HART communicator..

Answer / guest

Probably HART communicator used for online & onfield
calibration.As per my experience,I always used to do
calibration by step given bellow:
1.First,put transmitter loop in CAL mode.In CAL mode
controller the hold last PV for reference.causes without
stop or disturb process we can do calibration earlier
(depends on process)
2.Connect HART to the transmitter +ve & -ve
terminal.observed parameter on HART
display.e.g.pressure,dp,current output singnal.& note down.
3.Then close the isolation valve of both HP & LP tapping &
loose the both HP & LP side vent plug.In this condition
transmitter shoud show zero dp because same atmospheric
pressure actig both side.If transmitter showing zero dp
transmitter is normal & If it is not showing zero,then
there is some error in dp.
4.If transimtter showing error in dp then on HART go to
diagnosis-calibration-sensor calibration-dp trim.enter the
zero dp at atmospheric condition and come back on basic
setup display,transmitter will showing 4 mA current
output.means calibration is ok.then u can take transmitter
on line.and don't forget to checked leakage from impulse
tubing & vent plug.

Another procedure is Bench calibration.Using pressure &
calibrator we can check transmitter.even without HART we
can do bench calibration.

Is This Answer Correct ?    45 Yes 2 No

how can we calibrate the differential pressure transmitter by using HART communicator..

Answer / swapnil dhamanse

Probably HART communicator used for online & onfield
calibration.As per my experience,I always used to do
calibration by step given bellow:
1.First,put transmitter loop in CAL mode.In CAL mode
controller the hold last PV for reference.causes without
stop or disturb process we can do calibration earlier
(depends on process)
2.Connect HART to the transmitter +ve & -ve
terminal.observed parameter on HART
display.e.g.pressure,dp,current output singnal.& note down.
3.Then close the isolation valve of both HP & LP tapping &
loose the both HP & LP side vent plug.In this condition
transmitter shoud show zero dp because same atmospheric
pressure acting both side.If transmitter showing zero dp
transmitter is normal & If it is not showing zero,then
there is some error in dp.
4.If transimtter showing error in dp then on HART go to
diagnosis-calibration-sensor calibration-dp trim.enter the
zero dp at atmospheric condition and come back on basic
setup display,transmitter will showing 4 mA current
output.means calibration is ok.then u can take transmitter
on line.and don't forget to checked leakage from impulse
tubing & vent plug.

Another procedure is Bench calibration.Using pressure &
calibrator we can check transmitter.even without HART we
can do bench calibration.

Is This Answer Correct ?    10 Yes 2 No

how can we calibrate the differential pressure transmitter by using HART communicator..

Answer / deepak kumar

for DPT calibration on the field :
1.at first go the field and check our tag number to which u calibrate
2.then first close the both HP & HP side isolation valve,open the equaliser valve
3.open the vent valve
(for zero triming there is pressure flow)
4.then connect the HART communicator at ve and -ve terminal
5.open the hart =>>device setup=>>diagnosis=>>calibration=>>sensor calibration =>>dp trim=>>then enter Zero trim at atmospheric pressure
(that solve)
NOTE:-after complete the calibration close it to it's normal conditions..
.
thanx...

Is This Answer Correct ?    7 Yes 0 No

how can we calibrate the differential pressure transmitter by using HART communicator..

Answer / venkatesh

First do the 0 trime and span trim, In this it self problem
will solve....ealse use hand pump in point(In HP or LP side
it's deponds up on the usage) applay the pressure check the
reading

Is This Answer Correct ?    15 Yes 9 No

how can we calibrate the differential pressure transmitter by using HART communicator..

Answer / guest

ICON CONTROLS PVT. LTD.

Is This Answer Correct ?    10 Yes 6 No

how can we calibrate the differential pressure transmitter by using HART communicator..

Answer / malchom

You can not accurately calibrate a differential pressure transmitter with a HART communicator. A communicator is just that. A communicator, not a calibrator. The communicator is displaying to the user the pressure input and ma output units that the transmitter "thinks" it is seeing and sending. These values may be quite different than the actual values being applied and sent as indicated by pressure and current calibrators which have themselves been calibrated using a known standard. You can use the communicator to adjust the transmitter to then match your calibration equipment.

Is This Answer Correct ?    3 Yes 0 No

how can we calibrate the differential pressure transmitter by using HART communicator..

Answer / vimalraj

Hart communicator is a hart of DPT Transmitter.is not a calibirator .only we connect and see the pressure , range ,MA,%., units.and also we can modified the configuration of transmitter in online mode. if any major problem for a transmitter only we do that bench calibiration using by DRUK Calibirator or handpumb

Is This Answer Correct ?    1 Yes 0 No

how can we calibrate the differential pressure transmitter by using HART communicator..

Answer / praful lilhare

first of all connect the 250 ohm resistence in series while
connecting the HART to DPT for communication tnen close all
tabs and adjust zero.we can also adjust the range,unit by
using HART communicator.

Is This Answer Correct ?    6 Yes 6 No

Post New Answer

More Instrumentation Interview Questions

What are the type of bonnets in the control valves?

0 Answers   CCIE,


what is RPI and NUT in controlnet networx. what happen if we are increase the NUT of controlnet networx?

1 Answers   Schneider,


A flange is used for instrument connection for a system with a design temperature of 316&#61616;C (600&#61616;F) and a design pressure of 1000 kPa (145 psi). What is the class rating of the flange to be used for this application? Explain your answer

0 Answers  


what is meant by orderm of a system. will the stability of a system increases by incresing order of a system

1 Answers  


WHAT IS THE MASS FLOW FLOW METER

4 Answers   Reliance,


any one can send me instrumentation previous interview papers? I prepare for MNC Company Interviews? my mail id- Rakesh.Golla@dodsaldxb.ae , and another mail rakesh.gvk@gmail.com

0 Answers  


Q- What are the application in which PNP transistor is preferred over NPN ?

0 Answers  


I am applied 100 % pressure on to the air to open control valve,but the valve is not fully closed..and 10-15% is open the valve. how to calibrate the control valve?

3 Answers   OPaL,


Draw a great bridge circuit.

0 Answers   CCIE,


Can we used Condensate Pot on flow transmitter which is using on liquid having sluge and DP transmitter is in pit and below the process line,Can we used Condensate pot for accamulate the Sluge?

1 Answers  


Boiler flame scanner advantage?

0 Answers   Fluke, Petrochemicals, Tata Chemicals,


Hi buddies! my name is sachin and i am working as a electrical and instrumentation engineer in a paper plant. right now i am facing a problem and if someone could help me it will be an immense pleasure to me. i am using AC 800M to synchronise DCS500 drives on paper machine and rewinder.communication is on PROFIBUS and we are using NPBA-01 module to link profibus to DC drives.But these days two of these drives are showing a error named FIELDBUS COMM.TIMED OUT and the drives get tripped.I have changed the NPBA module and PROFIBUS cable.So if anyone can do please help me out with this problem.I'll be highly grateful.

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)