How to calculate transformer capacity requirement for a
project site?
Answers were Sorted based on User's Feedback
Answer / mahesh sali
THE CAPACITY OF TRANSFORMER USED FOR SITE APPLICATION SHALL
BE CALCULATED BY FOLLOWING CONSIDERATION;
CAL.TOTAL CONNECTED LOAD
BASE ON KW & ASSUMATION OF 0.8 P.F.
CAL. THE KVA/ MVA RATING OF X'MER I.E. KW/0.8
AFTER GETTING KVA/MVA ADD THE 20% IN CAL.KAV/MVA
I.E. KVA/MVA + 0.2*KVA/MVA
20% EXTRA AS PER IEEE RULE
AS PER IEEE NORM ,UR TRANSFORMER SHOULD BE LOADED AT 80% OF
UR FULL CAPACITY OF UR TRANSFOMER.
I HOPE ABOVE INF. IS SUFFICIENT.
THANKING U
| Is This Answer Correct ? | 26 Yes | 1 No |
Answer / vathnak kong
Example
We have Power load 2300KVA
So
Transformer Capacity=2300×1.4
1.4 is Power rate
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / sivaguru
Hi Mr.Mahesh
Can you please forward the IEEE rule showing the
transformer loading of 80% of full load as you
discussed....Kindly forward it to my email id
sivaguru_691984@yahoo.co.in...
Even we haven't took tr. loading factor for all our
projects and we will be really educated by pupil like you
for the need of consideration of transformer loading
factor...
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / thanigai1984
Now a days...
we calculated the connected load ...in KW and 40%
assumption load will be added
Transformer cap=60% load connected +40%
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / sunil biswal
Calculate all connected loads(KW) Assume Fans as 65Watt,15A sockets as 1000Watt, 5A Sockets at 1ooWatt, TV at 120 Watt Computer at 120Watt, Printer/Scanner/Copier at 1000Watt, A/C 1.5 Ton at 1.5KW
Apply diversity Factor since all loads will not be working at the same time always
Divide the single phase loads into 3 parts. (KW)
Then add three phase loads and i/3rd single phase loads(KW)
add 20% extra to this calculated gross KW
Divide by power factor 0.8 to get KVA Rating of transformer.
At this point you may add another 20% to the rating as a factor of safety and reliability since most machine work comfortably at 75 to 80% loading
Now decide the actual rating of transformer in proper slab as the standard ratings transformer are available in are 10KVA,16KVA,25KVA,63KVA,100 KVA, 125KVA, 160KVA, 200KVA, 250KVA, 500KVA in 11KV range.
| Is This Answer Correct ? | 1 Yes | 0 No |
what is the principal of braker
How to calculate kva? what is the formula.
21 Answers MSIL, UltraTech, Watt, Welding Aids,
why different series of vfds (like allenbradley)are used in industry ?
i am using star-delta connections with reverse/forward direction motion of the 75hp induction motor.What should be the ratings of Main,Delta and Star contactors and why?
what is the size of trasmission conducatar
What is Surge Capacitor? Why it is require in Generator Circuit Breaker,inspite of surge arrester?
A d.c. Shunt motor is found suitable to drive fans because they require?
DG use Rating KVA why
what are the main problems that happen in an emergency light and how to fix them ?
why designer use kva rating instead of kw in transformer rating???????????????
Why reactive power is needed in a power system? How is it being absorbed or delivered by alternators? For reactive power control we are changing excitation but reactive power absorbing or delivering related to stator. How these two are interlinked? i want a detailed explanation with necessary expressions and figures?
How much current flow in no load condition of a motor?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)