Why not instal the NGR in 11kv/433kv trasformer?
Answers were Sorted based on User's Feedback
Answer / mahesh sali
as per IEC norm the protection of 11 kv generator against
the earth fault current will be controlled by adding
external resistance between the star point of generator
winding & earth pits.
but for low voltage as per IEC has recommeded solidly
earthing system as per std.
Is This Answer Correct ? | 1 Yes | 0 No |
In my company we are generally using NGR for the secondary
side (433Voltage) of the Transformer....
Is This Answer Correct ? | 0 Yes | 0 No |
What is the reason behind 11kv 33kv 132kv.....means multiple of 11?
How you take care of a motor from over loading and what are the different overloading ratings of different motors?
What is a doble test
1 Answers KPSC Karnataka Public Service Corporation,
Can the efficiency of transformer be measured with the help of wattmeter readings taken at primary and secondary side? Support the answer.
what is the disaddvantages of high power factor
What is difference between incomer & outgoing type Vaccum Circuit Breaker?
Which ciass CT can be use in diff. protection. Can be use 5p20?
why we use isolation transformer?
what is fuction static switch in ups and tell me use parts name and fucion
How to work E.L.C.B and how to connect in circuit.
is KVAR (not reverse power) relay necessary to protect from excitor field failure on a brushless, synchroneus generator? Some people with previos experince tell me no but the manufacturers tell me it is designed for that purpose. Is it that it is only necessary for brushless generators and not the older style with the slip rings and brushes?
At what load maximum effiecency will be obtained Distribution transformer and Genarating transformer Pls clarify?